Results 1 to 13 of 16
    Jul 2012
    Phoenix, AZ
    Three stage cooling and Two stage heating.
    I helped install a new residential multistage heat pump system that was equipped to provide three stages cooling with two stages of heating. To be honest I really don’t understand how all the stages of heating and cooling were to be accomplished by the t-stat. I guess it’s something that I never picked up, or really understood but what I don't understand clearly is how or what controls the stages? Any takers?
    Saint Joseph, MI
    3 stages? How was that managed?
    You might need one of those little PLC type programmable controllers with display that has analog inputs and at least 6 digital outputs.
    Jan 2002
    Fayetteville, NC
    A digital t-stat with 5 relays could easly do it. Pretty easy really. Honeywell make 3H/3C t-stats. Not cheap thou.
    http://customer.honeywell.com/honeywell/productinfo.aspx/T7350H1009
    Sent from my DROIDX using Tapatalk 2
    Supermarket Tech...and anything else the boss finds for me!
    I do not understand how there would NOT be more stages of heat.
    You should have the same heat and cool from heat pump(in theory) as well as at least 1 stage of back up, maybe more.
    Jul 2012
    Phoenix, AZ
    Your right looking at it agian its 3heat and 3 cooling.
    Jan 2002
    Fayetteville, NC
    Mind you this is a guess, 3 compressors and 2 reversing valves.
    Saint Joseph, MI
    What brand?
    I'm really curious on this. I'm having trouble seeing the value over something like a Carrier Greenspeed.
    Maybe it's a two scroll unit with two refrigerant circuits and one of the scrolls unloads? But in heat, you only run with both loaded, since I think unloaded you don't gain any efficency in heating mode.
    Or a custom air handler with a A coil that has 2 refrigerant circuits and one of them is a 2 stage condenser.
    An interesting alternative when you think about it in applications where you want some redundancy and a sytem that rusn almost constantly or has a very small zone, but don't need more than 5 tons and are space limited to a single air handler. but it seems to me that an inverter unit would be better.
    Jul 2012
    Phoenix, AZ
    Trane.Trane.
    Jun 2001
    Are you absolutely sure it isn't the much more common 2 cool/3 heat?
    in a house, Appomattox, Va.
    maybe controlling two units off one tstat? a/c units and furnaces?
    I had a 3 cool, 2 heat a few yrs back. used a time delay for last stage.
    Col 3:23
    Jun 2010
    Nelson, Canada
    3H/2C
    This is quite common on geo systems and I would think on most air source HP's.
    Generally you would have a two stage compressor with two stages of heat and two of cool & 1 back up. I'm pretty sure most t-stats i've used have a time delay or a combination of temperature change over time for the back up/3rd stage relay.
    Saint Joseph, MI
    Quote Originally Posted by zacmobile View Post
    But he's talking about 3 cool, 2 heat. The vision pro IAQ will do 4heat, 2 cool. But I haven't seen one that will do 3 cool, there's not much demand for it.