Results 1 to 13 of 16
    Jul 2012
    Phoenix, AZ
    Three stage cooling and Two stage heating.
    I helped install a new residential multistage heat pump system that was equipped to provide three stages cooling with two stages of heating. To be honest I really dont understand how all the stages of heating and cooling were to be accomplished by the t-stat. I guess its something that I never picked up, or really understood but what I don't understand clearly is how or what controls the stages? Any takers?
    Saint Joseph, MI
    3 stages? How was that managed?
    You might need one of those little PLC type programmable controllers with display that has analog inputs and at least 6 digital outputs.
    Jan 2002
    Fayetteville, NC
    A digital t-stat with 5 relays could easly do it. Pretty easy really. Honeywell make 3H/3C t-stats. Not cheap thou.
    http://customer.honeywell.com/honeywell/productinfo.aspx/T7350H1009
    Sent from my DROIDX using Tapatalk 2
    Supermarket Tech...and anything else the boss finds for me!
    I do not understand how there would NOT be more stages of heat.
    You should have the same heat and cool from heat pump(in theory) as well as at least 1 stage of back up, maybe more.
    Jan 2002
    Fayetteville, NC
    Mind you this is a guess, 3 compressors and 2 reversing valves.
    Saint Joseph, MI
    What brand?
    I'm really curious on this. I'm having trouble seeing the value over something like a Carrier Greenspeed.
    Maybe it's a two scroll unit with two refrigerant circuits and one of the scrolls unloads? But in heat, you only run with both loaded, since I think unloaded you don't gain any efficency in heating mode.
    Or a custom air handler with a A coil that has 2 refrigerant circuits and one of them is a 2 stage condenser.
    An interesting alternative when you think about it in applications where you want some redundancy and a sytem that rusn almost constantly or has a very small zone, but don't need more than 5 tons and are space limited to a single air handler. but it seems to me that an inverter unit would be better.
    Jul 2012
    Phoenix, AZ
    Your right looking at it agian its 3heat and 3 cooling.
    Jul 2012
    Phoenix, AZ
    Trane.Trane.
    Jun 2001
    Are you absolutely sure it isn't the much more common 2 cool/3 heat?
    in a house, Appomattox, Va.
    maybe controlling two units off one tstat? a/c units and furnaces?
    I had a 3 cool, 2 heat a few yrs back. used a time delay for last stage.
    Col 3:23
    Jun 2010
    Nelson, Canada
    3H/2C
    This is quite common on geo systems and I would think on most air source HP's.
    Generally you would have a two stage compressor with two stages of heat and two of cool & 1 back up. I'm pretty sure most t-stats i've used have a time delay or a combination of temperature change over time for the back up/3rd stage relay.
    Saint Joseph, MI
    Quote Originally Posted by zacmobile View Post
    But he's talking about 3 cool, 2 heat. The vision pro IAQ will do 4heat, 2 cool. But I haven't seen one that will do 3 cool, there's not much demand for it.
