    Single row condenser coils. They look clean, but I'll be honest....I did not wash them.

  2. #28
    Join Date
    Sep 2004
    Posts
    13,930
    Post Likes
    317# head sounds high!
    true knowledge exists in knowing that you know nothing.

  3. #29
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,539
    Post Likes
    Thread Starter
    Went by and checked it yesterday. Its down to 280#. Its also 98* ambient in the shade.

  4. #30
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,309
    Post Likes
    317 on a unit that old 98 ambient is actually not that bad.

    Does that unit have the mechanical timer ?

  5. #31
    Join Date
    Sep 2004
    Posts
    13,930
    Post Likes
    135* SCT
    130* LLT
    005* SC
    079*SLT
    044* sst -74# SP
    035* SH

    HIGH EVAPORATOR TEMPERATURE
    130* LIQUID ENTERING EVAPORATOR
    HIGH EVAPORATOR CAPACITY
    LOW CONDENSER CAPACITY
    EXTREMELY LOW NET REFRIGERATION AFFECT

    it is clearly low on refrigerant, i would like to see how high the head is after he gets 12 * subcooling?







    Quote Originally Posted by Six View Post
    317 on a unit that old 98 ambient is actually not that bad.

    Does that unit have the mechanical timer ?
    true knowledge exists in knowing that you know nothing.

  6. #32
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,309
    Post Likes
    Quote Originally Posted by supertek65 View Post
    135* SCT
    130* LLT
    005* SC
    079*SLT
    044* sst -74# SP
    035* SH

    HIGH EVAPORATOR TEMPERATURE
    130* LIQUID ENTERING EVAPORATOR
    HIGH EVAPORATOR CAPACITY
    LOW CONDENSER CAPACITY
    EXTREMELY LOW NET REFRIGERATION AFFECT

    it is clearly low on refrigerant, i would like to see how high the head is after he gets 12 * subcooling?

    Lol....

    Liquid line is hot because units short charged and what does insuring a liquid seal in the condenser have to do with excessive head pressure. I'm not saying stack the coil with excessive refrigerant.

    So it's ok to short charge a system because you're afraid your going to launch the heads off the valve plates ? Charge the thing correctly and then see what your head pressures are.

    It's hackery . What does short charging do to a unit ? Lowers capacity, lowers efficiency causing the unit to run longer, can cause icing, poor cooling of the compressor windings, etc.

    Ive got an old York 20 ton and a old York 30 ton split ( installed in the late 80s ) with Copelands in them and they're properly charged, running high head ( 325,330 ) and they're still in one piece after 7 years of PMs.

  7. #33
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,539
    Post Likes
    Thread Starter
    Quote Originally Posted by Six View Post
    317 on a unit that old 98 ambient is actually not that bad.

    Does that unit have the mechanical timer ?
    Yea its got an old camstat timer

  8. #34
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,539
    Post Likes
    Thread Starter
    Quote Originally Posted by Six View Post
    Lol....

    Liquid line is hot because units short charged and what does insuring a liquid seal in the condenser have to do with excessive head pressure. I'm not saying stack the coil with excessive refrigerant.

    So it's ok to short charge a system because you're afraid your going to launch the heads off the valve plates ? Charge the thing correctly and then see what your head pressures are.

    It's hackery . What does short charging do to a unit ? Lowers capacity, lowers efficiency causing the unit to run longer, can cause icing, poor cooling of the compressor windings, etc.

    Ive got an old York 20 ton and a old York 30 ton split ( installed in the late 80s ) with Copelands in them and they're properly charged, running high head ( 325,330 ) and they're still in one piece after 7 years of PMs.
    I have never heard the term "short charged". What is that?

  9. #35
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,309
    Post Likes
    Yep, I've got three just like it. ( two 20s and a 30 )

    Old school controls with a choke coil to lower fan speed on the #1 condenser fan motor for capacity control.

    One of our EX-technicians wen't out on a service call and destroyed the control wiing inside the panel on the 30 when I was on vacation.

    I had to start from scratch to rebuild that panel.

  10. #36
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,309
    Post Likes
    Quote Originally Posted by socotech View Post
    I have never heard the term "short charged". What is that?
    Purposely under charging a unit to avoid high head trip or extended high head run time. ( I'm not saying you did that I just use the term to describe an undercharged unit in general )

    I don't believe in it. These Yorks I have have coils that are 2 pass and in horrible shape.

    They are charged to 12 to 14 degrees of subcooling and run fine and that's in Houston.

  11. #37
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,539
    Post Likes
    Thread Starter
    Ahhh yes. Short charge. I get it. Thats exactlly what I did. Afraid to blow the head of the compressor through my chest I guess. Learn something new everyday.

  12. #38
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,309
    Post Likes
    Quote Originally Posted by socotech View Post
    Ahhh yes. Short charge. I get it. Thats exactlly what I did. Afraid to blow the head of the compressor through my chest I guess. Learn something new everyday.
    I can understand the hesitancy to charge to correct subcooling when dealing with older coils and units in a hot climate but what will actually happen is your liquid line will cool down and you'll be providing your customer with 100 % of the capacity minus what it's lost because of it's general age.

    You will probably be surprised to see your head drop a little.

    Also you're Compressor amps will lower as you start cooling your wingdings more efficiently.

    I've gotten into a few debates over this with some of our fellow techs.

    You are not stacking refrigerant by providing a liquid seal and by providing a solid column of liquid to the TXVs, if your head DOES climb it's because you now have 100% capacity.


    Charge it to correct super heat and let it ride. All three of my antique Yorks are charged to 12 to 15 degrees of sub-cooling and ran fine through the heat wave we had last month.