  1. #27
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,365
    Single row condenser coils. They look clean, but I'll be honest....I did not wash them.

  2. #28
    Join Date
    Sep 2004
    Location
    Kansas City, Kansas, United States
    Posts
    13,833
    317# head sounds high!
    I WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
    YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!

  3. #29
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,365
    Went by and checked it yesterday. Its down to 280#. Its also 98* ambient in the shade.

  4. #30
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    317 on a unit that old 98 ambient is actually not that bad.

    Does that unit have the mechanical timer ?

  5. #31
    Join Date
    Sep 2004
    Location
    Kansas City, Kansas, United States
    Posts
    13,833
    135* SCT
    130* LLT
    005* SC
    079*SLT
    044* sst -74# SP
    035* SH

    HIGH EVAPORATOR TEMPERATURE
    130* LIQUID ENTERING EVAPORATOR
    HIGH EVAPORATOR CAPACITY
    LOW CONDENSER CAPACITY
    EXTREMELY LOW NET REFRIGERATION AFFECT

    it is clearly low on refrigerant, i would like to see how high the head is after he gets 12 * subcooling?







    Quote Originally Posted by Six View Post
    317 on a unit that old 98 ambient is actually not that bad.

    Does that unit have the mechanical timer ?
    I WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
    YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!

  6. #32
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    Quote Originally Posted by supertek65 View Post
    135* SCT
    130* LLT
    005* SC
    079*SLT
    044* sst -74# SP
    035* SH

    HIGH EVAPORATOR TEMPERATURE
    130* LIQUID ENTERING EVAPORATOR
    HIGH EVAPORATOR CAPACITY
    LOW CONDENSER CAPACITY
    EXTREMELY LOW NET REFRIGERATION AFFECT

    it is clearly low on refrigerant, i would like to see how high the head is after he gets 12 * subcooling?

    Lol....

    Liquid line is hot because units short charged and what does insuring a liquid seal in the condenser have to do with excessive head pressure. I'm not saying stack the coil with excessive refrigerant.

    So it's ok to short charge a system because you're afraid your going to launch the heads off the valve plates ? Charge the thing correctly and then see what your head pressures are.

    It's hackery . What does short charging do to a unit ? Lowers capacity, lowers efficiency causing the unit to run longer, can cause icing, poor cooling of the compressor windings, etc.

    Ive got an old York 20 ton and a old York 30 ton split ( installed in the late 80s ) with Copelands in them and they're properly charged, running high head ( 325,330 ) and they're still in one piece after 7 years of PMs.

  7. #33
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,365
    Quote Originally Posted by Six View Post
    317 on a unit that old 98 ambient is actually not that bad.

    Does that unit have the mechanical timer ?
    Yea its got an old camstat timer

  8. #34
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,365
    Quote Originally Posted by Six View Post
    Lol....

    Liquid line is hot because units short charged and what does insuring a liquid seal in the condenser have to do with excessive head pressure. I'm not saying stack the coil with excessive refrigerant.

    So it's ok to short charge a system because you're afraid your going to launch the heads off the valve plates ? Charge the thing correctly and then see what your head pressures are.

    It's hackery . What does short charging do to a unit ? Lowers capacity, lowers efficiency causing the unit to run longer, can cause icing, poor cooling of the compressor windings, etc.

    Ive got an old York 20 ton and a old York 30 ton split ( installed in the late 80s ) with Copelands in them and they're properly charged, running high head ( 325,330 ) and they're still in one piece after 7 years of PMs.
    I have never heard the term "short charged". What is that?

  9. #35
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    Yep, I've got three just like it. ( two 20s and a 30 )

    Old school controls with a choke coil to lower fan speed on the #1 condenser fan motor for capacity control.

    One of our EX-technicians wen't out on a service call and destroyed the control wiing inside the panel on the 30 when I was on vacation.

    I had to start from scratch to rebuild that panel.

  10. #36
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    Quote Originally Posted by socotech View Post
    I have never heard the term "short charged". What is that?
    Purposely under charging a unit to avoid high head trip or extended high head run time. ( I'm not saying you did that I just use the term to describe an undercharged unit in general )

    I don't believe in it. These Yorks I have have coils that are 2 pass and in horrible shape.

    They are charged to 12 to 14 degrees of subcooling and run fine and that's in Houston.

  11. #37
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,365
    Ahhh yes. Short charge. I get it. Thats exactlly what I did. Afraid to blow the head of the compressor through my chest I guess. Learn something new everyday.

  12. #38
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    Quote Originally Posted by socotech View Post
    Ahhh yes. Short charge. I get it. Thats exactlly what I did. Afraid to blow the head of the compressor through my chest I guess. Learn something new everyday.
    I can understand the hesitancy to charge to correct subcooling when dealing with older coils and units in a hot climate but what will actually happen is your liquid line will cool down and you'll be providing your customer with 100 % of the capacity minus what it's lost because of it's general age.

    You will probably be surprised to see your head drop a little.

    Also you're Compressor amps will lower as you start cooling your wingdings more efficiently.

    I've gotten into a few debates over this with some of our fellow techs.

    You are not stacking refrigerant by providing a liquid seal and by providing a solid column of liquid to the TXVs, if your head DOES climb it's because you now have 100% capacity.


    Charge it to correct super heat and let it ride. All three of my antique Yorks are charged to 12 to 15 degrees of sub-cooling and ran fine through the heat wave we had last month.

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event