Page 3 of 3 FirstFirst 123
Results 27 to 38 of 38
  1. #27
    Nov 2007
    Mississippi
    Single row condenser coils. They look clean, but I'll be honest....I did not wash them.
  2. #28
    317# head sounds high!
  3. #29
    Nov 2007
    Mississippi
    Went by and checked it yesterday. Its down to 280#. Its also 98* ambient in the shade.
  4. #30
    Apr 2012
    Paper Street Soap Company
    317 on a unit that old 98 ambient is actually not that bad.
    Does that unit have the mechanical timer ?
  5. #31
    135* SCT
    130* LLT
    005* SC
    079*SLT
    044* sst -74# SP
    035* SH
    HIGH EVAPORATOR TEMPERATURE
    130* LIQUID ENTERING EVAPORATOR
    HIGH EVAPORATOR CAPACITY
    LOW CONDENSER CAPACITY
    EXTREMELY LOW NET REFRIGERATION AFFECT
    it is clearly low on refrigerant, i would like to see how high the head is after he gets 12 * subcooling?
    Quote Originally Posted by Six View Post
  6. #32
    Apr 2012
    Quote Originally Posted by supertek65 View Post
    135* SCT
    130* LLT
    005* SC
    079*SLT
    044* sst -74# SP
    035* SH
    Lol....
    Liquid line is hot because units short charged and what does insuring a liquid seal in the condenser have to do with excessive head pressure. I'm not saying stack the coil with excessive refrigerant.
    So it's ok to short charge a system because you're afraid your going to launch the heads off the valve plates ? Charge the thing correctly and then see what your head pressures are.
    It's hackery . What does short charging do to a unit ? Lowers capacity, lowers efficiency causing the unit to run longer, can cause icing, poor cooling of the compressor windings, etc.
    Ive got an old York 20 ton and a old York 30 ton split ( installed in the late 80s ) with Copelands in them and they're properly charged, running high head ( 325,330 ) and they're still in one piece after 7 years of PMs.
  7. #33
    Nov 2007
    Mississippi
    Yea its got an old camstat timer
  8. #34
    Nov 2007
    Mississippi
    Lol....
    I have never heard the term "short charged". What is that?
  9. #35
    Apr 2012
    Yep, I've got three just like it. ( two 20s and a 30 )
    Old school controls with a choke coil to lower fan speed on the #1 condenser fan motor for capacity control.
    One of our EX-technicians wen't out on a service call and destroyed the control wiing inside the panel on the 30 when I was on vacation.
    I had to start from scratch to rebuild that panel.
  10. #36
    Apr 2012
    Quote Originally Posted by socotech View Post
    Purposely under charging a unit to avoid high head trip or extended high head run time. ( I'm not saying you did that I just use the term to describe an undercharged unit in general )
    I don't believe in it. These Yorks I have have coils that are 2 pass and in horrible shape.
    They are charged to 12 to 14 degrees of subcooling and run fine and that's in Houston.
  11. #37
    Nov 2007
    Mississippi
    Ahhh yes. Short charge. I get it. Thats exactlly what I did. Afraid to blow the head of the compressor through my chest I guess. Learn something new everyday.
  12. #38
    Apr 2012
    I can understand the hesitancy to charge to correct subcooling when dealing with older coils and units in a hot climate but what will actually happen is your liquid line will cool down and you'll be providing your customer with 100 % of the capacity minus what it's lost because of it's general age.
    You will probably be surprised to see your head drop a little.
    Also you're Compressor amps will lower as you start cooling your wingdings more efficiently.
    I've gotten into a few debates over this with some of our fellow techs.
    You are not stacking refrigerant by providing a liquid seal and by providing a solid column of liquid to the TXVs, if your head DOES climb it's because you now have 100% capacity.
    Charge it to correct super heat and let it ride. All three of my antique Yorks are charged to 12 to 15 degrees of sub-cooling and ran fine through the heat wave we had last month.