York DH150N15Q2BMA3D
This system keeps going out on high head pressure for both circuits (400psig). Both condenser fans are running, and both coils are clean. When I spray a hose with water on the condenser coil and have it run it runs just fine, but as soon as I shut the water off it go's out on high head?
It just started today, but could it be low on charge? It's not even 100 out like it was last week, and didn't have a problem.
Sent from my iPhone using Tapatalk
-
07-30-2012, 07:06 PM #2
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 916
Are you sure both fans are spinning the right way?
Could be a bad cap making 1 spin the wrong way.
-
07-30-2012, 07:17 PM #3
Maybe, so here is a picture of the caps, the one thing I'm not liking is they don't say which cap is for with fan motor.
Sent from my iPhone using Tapatalk
-
07-30-2012, 07:48 PM #4
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 916
Read the wiring diagram, that will tell you.
Or pull wires off and see which one won't run.
-
07-30-2012, 07:51 PM #5
Boss called and said just replace both caps since I'm there, they both read 9.5mdf and there 10mdf
Sent from my iPhone using Tapatalk
-
07-30-2012, 07:51 PM #6
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 916
Have you checked rotation or at least stuck you hand over the blades. You should be able feel the air is not right.
Or shut the unit off when it's running and look at the blades as there slowing down.
-
07-30-2012, 07:53 PM #7
After replacing both now it's running and hasn't gone out on high head pressure as of yet
Sent from my iPhone using Tapatalk
-
07-30-2012, 09:13 PM #8
I would clean the coil. I have had many that were "clean" but when you actually clean it the dirt poors out.
Sent from my iPad using Tapatalk HDTo the man who always did it right. I love you dad and I will miss you to much for words.
Stay Thirsty My Friends
Support the Skilled Trades Don't DIY
-
07-30-2012, 09:17 PM #9
I cleaned the coil when I first got there and didn't get any major dirt to come out. Cause that was my first though that it was dirty coils.
We just had one of the other techs do roof PM all all the condensors and Evaps for all the rooftop units less than a month ago.
-
07-30-2012, 11:28 PM #10
Never assume the other tech did his job properly. Just because a coil looks clean, doesn't mean it is. Not to be condescending, but do you know how to tell if a fan is running the proper rotation? I have run into techs who don't know. In fact, I'm training one right now.
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
07-30-2012, 11:35 PM #11
I didn't notice right off the bat, but I put my hat over both fans I noticed that one fan was trying to force my hat to fly out of my hand while the other one was sucking my hat down. So I then changed out both caps since they both tested at 9.5mdf when they were 10mdf, once I did that they both were trying to make my hat fly out of my hand.