Results 1 to 20 of 20

Thread: How to deal with doors opening and closing -- letting in hot air?

  1. #1
    Join Date
    Sep 2007
    Location
    Sarasota/Bradenton, FL
    Posts
    56
    Post Likes

    How to deal with doors opening and closing -- letting in hot air?

    So, I'm in the process of re-thinking my A/C. I may simply be replacing a unit (one of three), or just re-designing the whole darn thing.

    Hence, I'm asking all sorts of questions.

    I'm a slightly strange homeowner -- HVAC problems actually keep me awake at night!

    In any case, and this is a question I've pondered over the years, here goes...

    How does one best deal with an area in a house that gets a lot of exposure to the outside?

    In my own house I have three such areas. This is South West Fla.

    1) A laundry room, right off the kitchen, that leads to the garage. We are going in and out constantly. At times, we go in and out so often, that the door might as well be open full time.

    2) A living room. Very large, 20' X 20', but communicates with the pool area. So, when the pool is in use, the kids are in and out non-stop.

    3) A bedroom. Right by the pool. Less use but still, the door is letting in a lot of outside air.

    In short, we live a very indoor/outdoor lifestyle.


    I've thought of two solutions:

    1) Just install an additional, large, regular A/C return over each entrance.

    2) Over each often-used entrance (inside the house, I mean), for example in the laundry room foyer, I could install an in-line fan. It would be exhausted to the outside. I would run it at low CFMs, say 20-40CFM -- but constantly.

    Negative pressure is not a problem, because we're coming and going so often. But, if each area that get open to the outside all the time, has an exhaust fan, less of the hot, not-conditioned air gets into the house. Or so I'm thinking??


    Thoughts?

    And all input is always very carefully considered, and much appreciated!! (And will keep me awake...considering...things...)


    b (Thanks!)

  2. #2
    Join Date
    Jul 2012
    Posts
    12
    Post Likes

    Perhaps think of your home as a walk-in cooler??

    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.
    Last edited by jpsmith1cm; 07-30-2012 at 09:31 PM. Reason: Non AOP Member

  3. #3
    Join Date
    Jun 2010
    Location
    Philadelphia PA
    Posts
    2,209
    Post Likes

    You need a small chiller

    so you can get some cold water and pick coils that can handle the high latent load. Pool that communicates to living space with kids splashing around and you have AC and expect residential equipment to do the job...

    Good Luck
    You have got to learn from other people's mistakes! Because God knows you don't live long enough to make them all yourself !!!!!!!!

  4. #4
    Join Date
    Jul 2012
    Posts
    12
    Post Likes
    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.
    Last edited by jpsmith1cm; 07-30-2012 at 09:31 PM. Reason: Non AOP Member

  5. #5
    Join Date
    Jul 2012
    Posts
    12
    Post Likes
    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.
    Last edited by jpsmith1cm; 07-30-2012 at 09:32 PM. Reason: Non AOP Member

  6. #6
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Frank-0

    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.



  7. #7
    Join Date
    Sep 2007
    Location
    Sarasota/Bradenton, FL
    Posts
    56
    Post Likes
    Thread Starter
    Quote Originally Posted by genduct View Post
    so you can get some cold water and pick coils that can handle the high latent load. Pool that communicates to living space with kids splashing around and you have AC and expect residential equipment to do the job...

    Good Luck
    Hmmm...

    Sounds a bit hopeless.

    But, at the same time, I'm thinking that I can't be the first homeowner in Fla to have this problem.

    Also, I'm not sure what a small chiller is?

    Installing an extra return in foyer, over the door to the garage that gets a lot of use was actually the suggestion of a pro who came to service my A/C.

    And the idea of continuous, low CFM exhaust was my own idea.

    I'm kind of leaning toward the continuous, low CFM (25 or so) idea.

    What I'm thinking is that exhausting at low CFMs to the outside won't affect the A/C too much. But, it will pull out the hot, humid air that rises to the ceiling.

    I mean, the door opening/closing itself dumps all sorts of air in and out.

    A return over that area would mess with the balance of the A/C more, I would guess.

    And air curtain would be nice -- or any other commercial solution. But, I don't know if that's realistic for me at this point...

    Any thoughts?

  8. #8
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,115
    Post Likes
    Have you given any thought to an air curtain? Very uncommon in residential but would help slow down air transfer through the openings like they edo at freight doors.

  9. #9
    Join Date
    Jul 2004
    Location
    Massachusetts
    Posts
    6,846
    Post Likes
    You need a good contractor who's not afraid to install one of the new modulating heat pumps. If you were my client, I'd recommend a zone control system, coupled with an over sized heat pump such that when high load demands are present, the system has the capacity to do the job. By over sizing you'll also be able to get very efficient heat at colder temperatures than a normally properly sized HP but at the same time, being able to reduce to 30% of maximum output will make sure the system isn't over sized for summer cooling and so can do a great job of dehumidifying your home. The ducts will need to be re-worked to accommodate the areas that are currently problematic due to outdoor air infiltration but a sophisticated zone system can easily handle the variable needs of each zone. We're a Bryant dealer so I am most knowledgeable about the Carrier/Bryant line. In keeping with that, I'd recommend a Bryant Extreme heat pump, Evolution zone control system and re-work of ducts as needed to accommodate the system over sizing. You'll be pleasantly surprised at the new found comfort and overall substantially reduced operating costs. You'll also be surprised at the sticker price so please be sitting down when you get the quote. It's going to cost but the results are well worth it. To get things into perspective, I'd say the costs to acquire a properly designed and installed system will be on the order of the cost of a small Lexus auto or less.
    If YOU want change, YOU have to first change.

    If you are waiting for the 'other guy' to change first, just remember, you're the 'other guy's' other guy. To continue to expect real change when you keep acting the same way as always, is folly. Won't happen. Real change will only happen when a majority of the people change the way they vote!

  10. #10
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    +1 on either a modulating heat pump like a Carrier Greenspeed, or replace all 3 with a single VRF system with 3 indoor air handlers such as those by Mitsubishi or Daikin.

    The 2nd option since it's a larger home that needs 3 systems and has high humidity and varyign loads, is putting in a chiller with 3 or more seperate fan coils possibly with hot water reheat as well off of a hot gas reheat system making hot water or a natural gas wall boiler. You can even use the chiller to heat the pool water as well with a seperate heat exchanger.

    FYI - a chiller is just like a air conditioner, but instead of cooling air, it cools water. All larger commerical and industrial that need cooling and are designed correctly and effciently, use chillers in warm and hot climates.

    That beign said, chillers, while prviding better year round comfort and dehumidification, and lower overall operating costs on larger systems, are not cheap. The Bryant and Carrier Inverter drive system like the Greenspeed and Extreme, might be more econimical overall.


    I wouldn;t specifically modify the ductowrk. IF anything I'd add a supply near and exterior exit, not a return. A return will increase the amoutn of air that leaks into the home when the door is open and could cause mold in the return ductowkr. A supply on a system that runs continously at low speed will help pressurize the space to keep the hot humid air out. However, you may also get some sweating on the registers too. I would use plastic registers if possible in thseo locations.

  11. #11
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Just put one of these over each door that gets heavy use:

    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  12. #12
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    Hmmm commerical air curtain. Nice idea.

  13. #13
    Join Date
    May 2004
    Location
    south louisiana
    Posts
    3,790
    Post Likes
    I thought air curtain also.
    as did poster #8, 11 & 13.

    limit numbers of doors used to buy less air curtains.

    best of luck.
    The cure of the part should not be attempted without the cure of the whole. ~Plato

  14. #14
    Join Date
    Mar 2009
    Location
    Mount Holly, NC
    Posts
    9,064
    Post Likes
    a poor man's air curtain would be to have a return set outside to positive pressure the house. it's commonly called fresh air makeup.
    The TRUE highest cost system is the system not installed properly...

    Find a HVAC-Talk Contractor by clicking here

    Click below to BECOME a pro member
    https://hvac-talk.com/vbb/forumdispl...ip-Information

    Do you go to a boat repairman with a sinking boat, and tell him to put in a bigger motor when he tells you to fix the holes?

    I am yourmrfixit

  15. #15
    Join Date
    Jun 2010
    Location
    Philadelphia PA
    Posts
    2,209
    Post Likes

    The Pool thing changes everything

    A living room. Very large, 20' X 20', but communicates with the pool area. So, when the pool is in use, the kids are in and out non-stop.

    3) A bedroom. Right by the pool. Less use but still, the door is letting in a lot of outside air.
    The POO: makes this a situation with a latent load that is offf the charts and more of a commercial application
    A chiller produces cold water and you can select coils that will deal with the high latent load whate "standard equipment will NOT

    Sorry to mention this but everyone in Fl has a pool that communicates with their living space, if I understand your post
    You have got to learn from other people's mistakes! Because God knows you don't live long enough to make them all yourself !!!!!!!!

  16. #16
    Join Date
    Jul 2012
    Posts
    12
    Post Likes
    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.
    Last edited by jpsmith1cm; 08-02-2012 at 05:46 AM. Reason: non-AOP member

  17. #17
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Frank-O

    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.



  18. #18
    Join Date
    Oct 2009
    Location
    Florida
    Posts
    201
    Post Likes
    What if you positively pressurize the house? Any door open would push cold air out instead of hot air in.

  19. #19
    Join Date
    Jul 2007
    Location
    Beautiful, Philadelphia, the City of Brotherly Love!
    Posts
    1,264
    Post Likes
    Why not build an addition over your pool area bringing it inside.

  20. #20
    Join Date
    Sep 2007
    Location
    Sarasota/Bradenton, FL
    Posts
    56
    Post Likes
    Thread Starter
    This has been very useful. If for no other reason than this...
    Of the 4-5 pros I've had look at the house, only one offered the Bryant Extreme, and at a fairly reasonable price.

    But the idea of air curtains really makes sense -- short of redesigning the system.

    My question about that is, do they have to be mounted on the inside? I've looked at some sites, and they all seem to be inside mount. Trouble is, all the door in my house open to the inside. Is that a problem?

    Thanks!

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •