    Need a good wireless stat for a commercial application

    I need to find a good wireless t-stat to control two stages of cooling and two stages of heat for a carrier RTU. It is located on the roof of a bank. There is a short in the wiring and pulling a new one would be a ton of work. Thanks in advance.


    Sent from my iPad using Tapatalk HD
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  2. #2
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,107
    I guess no one has an answer?


    Sent from my iPhone 4s
    using Tapatalk
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  3. #3
    Join Date
    Feb 2010
    Location
    In a boiler room
    Posts
    7,119
    Honeywell? They should have a multi stage wireless stat.

  4. #4
    Join Date
    Dec 2002
    Location
    Arizona
    Posts
    4,410
    Make your expertise uniquely valuable.

    Make your influence uniquely far-reaching.

  5. #5
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,107
    Quote Originally Posted by jimj View Post
    That is exactly what I was looking for. Have you used this stat yet and if so has it been reliable?


    Sent from my iPad using Tapatalk HD
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  6. #6
    Join Date
    Dec 2002
    Location
    Arizona
    Posts
    4,410
    Its works well as long as the control module is not mounted in a metal enclosure.
    Make your expertise uniquely valuable.

    Make your influence uniquely far-reaching.

  7. #7
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,107
    Great. I can mount it in the mechanical room on the mezzanine that is above the teller line. This should work perfect.


    Sent from my iPad using Tapatalk HD
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  8. #8
    Join Date
    Jan 2002
    Location
    Palatine Il.
    Posts
    393
    The Honeywell Focus Pro 5000 (non programmable) and 6000 (programmable) wireless stats will do 2 stage operation. We have used these in many residential and commercial applications with 0 failures.

    Also, if any 2 of your wires are still useable, you can use the Honeywell Prestige IAQ 2.0, which only needs two wires to power the stat, and otherwise is wireless to the control module. The Prestige 2.0 gives you many more options, including the addition of wireless remote sensors if needed. And yes the 2.0 can be resi of commrecial use, you just have to choose which in the set up menu.
    Hi, my name is Glenn, and I'm a Toolaholic!

  9. #9
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,107
    Quote Originally Posted by Glenn Harrison View Post
    The Honeywell Focus Pro 5000 (non programmable) and 6000 (programmable) wireless stats will do 2 stage operation. We have used these in many residential and commercial applications with 0 failures.

    Also, if any 2 of your wires are still useable, you can use the Honeywell Prestige IAQ 2.0, which only needs two wires to power the stat, and otherwise is wireless to the control module. The Prestige 2.0 gives you many more options, including the addition of wireless remote sensors if needed. And yes the 2.0 can be resi of commrecial use, you just have to choose which in the set up menu.
    Thanks for info Glenn.


    Sent from my iPad using Tapatalk HD
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  10. #10
    Join Date
    Aug 2012
    Location
    MA
    Posts
    39
    Quote Originally Posted by chuckcrj View Post
    Honeywell? They should have a multi stage wireless stat.
    Honeywell makes a great wireless stat that can also communicate with a multi zone board...

  11. #11
    Join Date
    Jul 2012
    Location
    Southwest
    Posts
    114
    I have installed 20+ Honeywell 6000's with 0 failures.