    I got a call on sunday about a recent install several hours out of town. The system is condensing on the outside of the plenum and on the lowside of the lineset so much that it is pooling on the floor and seeping under the wall. I am looking for possible causes/solutions to prep myself because it is so far away. Anyone got any suggestions?

  2. #2
    Join Date
    Jan 2002
    Location
    Fayetteville, NC
    Posts
    206
    Post Likes
    Has the suction line and plenum been insulated?

    Sent from my DROIDX using Tapatalk 2
    Supermarket Tech...and anything else the boss finds for me!

  3. #3
    Join Date
    Jul 2012
    Location
    Peace River, Alberta, Canada
    Posts
    46
    Post Likes
    Thread Starter
    Suction yes, plenum no

  4. #4
    Join Date
    Jun 2009
    Location
    Upstate SC
    Posts
    1,439
    Post Likes
    Insulate plenums and condensate drain.

    Sent from my ERIS using Tapatalk 2

  5. #5
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    8,666
    Post Likes
    If the home is <45%RH inside after a couple hour run, increase your fan speed a little. This will warm the air in the ducts a little and reduce condenstion. If %RH in the 50% area, overinsulate the ducts/suction with more insulation. Make sure good vapor barrier on the outside of the insulation to prevent moisture infiltration.
    Regards TB
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  6. #6
    Join Date
    Dec 2007
    Location
    north suburbs of Chicago
    Posts
    1,626
    Post Likes
    If this is in a basement you may have very high humidity down there. It's probably quite cool too which only adds to the problem. A dehumidifier maybe. Also cutting in a low return or two in the basement helps in many ways. Air flow, dehumidification, and warming in winter by giving that cold a place to go.