    Checking numbers
    Got a 4 ton unit that is acting up on me. Below are my numbers:
    Outdoor DB=92
    Suction Pressure=82
    Discharge pressure 235
    Liquid line temp=110
    Suction line temp=68
    Indoor DB=73.5
    ID WB=64
    Compressor amps 10.5 out of a fla of 14
    Cap tube system
    A superheat of 20 is telling me that I am undercharged when my target should be about 7 degrees. Does this sound like I am on the right track?
    Jul 2012
    San Francisco Bay area
    Whats the delta T across the evap
    10 degrees
    Jul 2012
    little low on charge just need to recheck the superheat after space temp gets down to setpoint
    Jul 2012
    go for 12 sh
    Jan 2012
    WEST COLUMBIA S.C.
    What type of metering device and what is your supply and return temp.I ASSUME this is a R22 system based on pressures?
    Cap tube system with 73.5 return and 64 supply. It is an r-22 system.
    Nov 2010
    N. Idaho
    My TSH shows somewhere around 7, with the conditions you stated. I'd say you're on the right track
    "I've got my Gas Mechanics license"
    "Yea, well my 16yr old daughter has her drivers license, doesn't mean she knows how to drive"
    Is the ductwork tight?
    Jan 2012
    WEST COLUMBIA S.C.
    What is your cfm at return
    Jul 2005
    You have a bad (under-pumping) compressor. High suction, low head, low amp draw, low deltaT. Adding refrigerant will only run the suction pressure up higher, and it's already way to high for those conditions on an old cap tube system.
    Jan 2012
    WEST COLUMBIA S.C.
    X2
    Jul 2009
    South Carolina
    The only way it would be undercharged is if you were sucking air from the attic across the evaporator. If the temps you measured are what are actually going across the evaporator then I agree with Hvacrmedic, you have a weak compressor.
    Gary
    http://www.oceanhvac.com
    An engineer designs what he would never work on.
    A technician works on what he would never design.