Results 1 to 13 of 25
Thread: Cvhve oil log ref??"??
-
07-29-2012, 08:43 AM #1
Professional Member
- Join Date
- Jan 2011
- Location
- tt, west indies
- Posts
- 118
Cvhve oil log ref??"??
Opened up system to change oil and clean inside oil drum after oil analysis (found dirt),replaced rear bearings , cuz of hi brg temp, started system purged , added some refrigerant(123) got system down to 50degf but it refuses to go lower .
Customer said they were losing oil before and added abt 27 gallons of oil because the oil level kept droping which was probably due to ejectors, so here r the temps n approaches.lwt51
Retchw-59
Ent con-94degf
Levcon-104
Evap-18hg
Con press-14psi
Condensin temp 116
Condensin temp in 107
-
07-29-2012, 10:37 AM #2
-
07-29-2012, 10:40 AM #3
Professional Member
- Join Date
- Jan 2011
- Location
- tt, west indies
- Posts
- 118
-
07-29-2012, 10:42 AM #4
Professional Member
- Join Date
- Jan 2011
- Location
- tt, west indies
- Posts
- 118
-
07-29-2012, 10:58 AM #5Spellin mitsakes bother me.
-
07-29-2012, 11:09 AM #6
Professional Member
- Join Date
- Jan 2011
- Location
- tt, west indies
- Posts
- 118
So still either way I'd still hav to pull the charge ,but if it was low on charge and vanes fully open it should have surged ,and condensing press n saturation temp would have been lower? So I think I'm right back to where I feared. To go I can't afford to shut that machine down this building takes abt 5 days to recover
-
07-29-2012, 02:39 PM #7
not necessarily. oil inhibits heat transfer which helps keep your condensing temperature and pressure high. i have yet to see a properly running machine with the vanes at 100% and fully loaded...it is possible i suppose, but i would be very suspect if the vanes needed to be that far open at full load.
Spellin mitsakes bother me.
-
07-29-2012, 03:09 PM #8
Professional Member
- Join Date
- Jan 2011
- Location
- tt, west indies
- Posts
- 118
Oil drum is filled way past sight glass , so I'm thinking if reduce the oil charge to a lower level not to low do you think the ejector/eductor will sip the oil that's in the evap and fill back the drum and give me a little more efficency?I'm at the job site now and this jus dawned on me what do u think?
-
07-30-2012, 07:53 AM #9
Professional Member
- Join Date
- Jun 2010
- Location
- Tampa, FL
- Posts
- 96
If you must keep the machine on line, drain oil to bottom of lower sight glass. Come back once a day and drain more oil until conditions improve and oil level is no longer rising. You need some vapor space in oil tank for system to work right. How did oil leave? Slow or fast. Some things to check: Eductor operation, oil tank vent line solenoid, restricted return line from suction cover,oil tank temp/heater, oil pressure, worn oil seals,refrigerant overcharge w/carryover. Why are cond temps so high? Get temps to about 85/95.
-
07-30-2012, 08:04 AM #10
Professional Member
- Join Date
- Jan 2011
- Location
- tt, west indies
- Posts
- 118
Dropped oil level it filld back up twice the second time the vent soloniod opened,left system running wit oil at half of sight glass oil left fast but its stedy now, water temps have dropped to 51/61 quickly and settles at that and machince amperager draw is running between 380and 400 (flucuating fast) evap press is 18hg con is 14.con is 94/101
-
07-30-2012, 08:18 AM #11
Professional Member
- Join Date
- Jan 2011
- Location
- tt, west indies
- Posts
- 118
-
07-30-2012, 08:49 AM #12
Professional Member*
- Join Date
- Aug 2009
- Location
- Prattville,Alabama
- Posts
- 1,102
I know you're worried about getting chill water temps into the 40's, but don't let that cause you to ignore everthing else. The 2 most obvious problems you appear to have are oil saturated refrigerant and high entering condenser water temps. If you must keep chiller on line, deltap10's advice is good. However it is slow. But at least you can maintain 51 degrees that way. You should quickly work to resolve the problem with the high entering condenser water temperature. That will give immediate results and improvement. That is, assuming you can quickly lower that temp to 85 F or less. Also, the condenser pressure is high for the saturated condensing temperature. Verify proper purge operation. There may be air in the chiller.
-
07-30-2012, 09:06 AM #13


Reply With Quote
taut It could hav been something else