Results 1 to 10 of 10
    May 2012
    Alerton Interface with BACnet/IP
    I have one project using envision 2.6 and BCM-ETH, I have to integrate with micron fire alarm system, they are using BACnet/IP I tried to scan their gateway using device scan in envision but only my Alerton controllers are shown, I tried to scan using third party CAS Bacnet explorer it got both Alerton and Micron networks, but Alerton netwrok came under BACnet/Ethernet and Miccron came under BACnet/IP.
    Is there any settings I have to do to succefully scan their system, all the physical connections are OK IP's are OK.
    Is there any difference between Bacnet/IP & Bacnet/Ethernet?
    I'm not an Alerton proffessional as this is my first time to work with Alerton system.
    Any help will be highly appreciated, thanks.
  2. Likes dipak c liked this post
  3. #2
    Council Bluffs, Iowa
    You are going to have to get into the general system setup in the Envision front end and also hyper terminal into the BCM-Eth. They have the system setup to run Bacnet over Ethernet instead of Bacnet/IP. Its easy to change if you know Alerton.
  4. Likes dipak c liked this post
  5. #3
    Nov 2005
    Shreveport, Louisiana
    Bacnet Ethernet is only on one subnet and cannot pass routers, Bacnet IP is well just as it says.
    UA Local 141
  6. #4
    May 2012
    Urgent
    Thanks CB_Matt & Berg2666, if I changed the envision and the BCM-ETH from BAcnet/ETH to BACnet/IP, I have to make all the commissioning activities for the VLC's again??
  7. #5
    No. It should not have any effect on the VLC's
  8. #6
    May 2012
    After Success in discovering points
    I'll try this after the weekend, so if I have the point list with me, what I have to do offline, should I make a program using Visio and if so it will be only soft I/O points, and if so where I have to download it; in the BCM?
    and in case I want to show the points in graphics only, what I have to do?
  9. #7
    Jan 2016
    Please Can you show us how you configure BCM ETH as Bacnet IP?
  10. #8
    Dec 2006
    What? Who? Where?
    Quote Originally Posted by Darweesh View Post
    Null modem cable and Hyper-Terminal.
    kontrol out
    "Good" - Jocko
    "Open is as open does." - Forrest Gump
    "Can't we all just get a Lon?" - Garry Jack
    "BACnet: integration or interrogation?" - The Janitor
    "Open protocols? You can't handle open protocols!" - Nathan R. Jessup
    “What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora Watch it here!
  11. #9
    Oct 2013
    Like Kontrol said, you need to connect the BCM-ETH to your PC's serial (COM) port using a null modem cable. Open hyperlink and set baud rate to 57600, stop bits 1, parity none. press enter and you should get the configurations menu of the BCM-ETH. default password is pass. Ones you get in you should see the menus to configure IP addresses, enable/disable Bacnet/IP etc.
  12. #10
    Sacramento, CA
    Quote Originally Posted by Aladdin View Post
    You can make the BCM (global) program offline. It has only software points, but it can read/write any point in the system. We typically use BCM ddc to gather heating/cooling demand, etc.
    Download the ddc via Device Manager.
    Alerton has their own built-in display editor. Check the manual.