    I know that the presuures must be converted to temp for superheat and subcooloing For superheat is the suction line temp read at condenser or evap? For subcoolong is the temp read at condenser or evap. My boss tells me one and another tech tells me another. I'm new and learning in this field but everyone has a different way of doing. Thanks

  2. #2
    Join Date
    Jul 2005
    Post Likes
    subcooling is on the liquid side or high side at the condenser

    superheat is at the evap or low side at the service valve at or near the compressor
    once you think you've seen it all
    I would rather work for free than be look upon as a thief!!!!!

  3. #3
    Join Date
    Mar 2006
    cincinnati, ohio
    Post Likes
    both at the service valves by the compressor
    Knowledge comes with experience