I know that the presuures must be converted to temp for superheat and subcooloing For superheat is the suction line temp read at condenser or evap? For subcoolong is the temp read at condenser or evap. My boss tells me one and another tech tells me another. I'm new and learning in this field but everyone has a different way of doing. Thanks
-
08-26-2006, 08:31 AM #2
Professional Member
- Join Date
- Jul 2005
- Location
- FLORIDA
- Posts
- 1,162
subcooling is on the liquid side or high side at the condenser
superheat is at the evap or low side at the service valve at or near the compressoronce you think you've seen it all
(THINK AGAIN)
I would rather work for free than be look upon as a thief!!!!!
-
08-26-2006, 08:33 AM #3
both at the service valves by the compressor