07-29-2012, 04:57 PM #14
If it is locked up replacing bearings will be a waste of time. Chances are the rotors are damaged and so would the housing.
-
07-29-2012, 05:14 PM #15
Regular Guest
- Join Date
- Jun 2011
- Location
- Chicago,il
- Posts
- 17
i havent started looking for the oil yet, any ideas anyone. i know its not on the ground and its not in the seperator. its a rtac
-
07-29-2012, 06:19 PM #16
Professional Member
- Join Date
- May 2002
- Location
- evansville indiana
- Posts
- 892
Its in there ....evap maybe would be my guess....
http://www.trane.com/CPS/uploads/use...N_02172011.pdfmikeacman
-
07-29-2012, 06:53 PM #17
-
07-30-2012, 06:00 AM #18
Professional Member
- Join Date
- May 2002
- Location
- evansville indiana
- Posts
- 892
-
08-11-2012, 10:36 AM #19
Professional Member
- Join Date
- Jan 2005
- Posts
- 61
you said it come on? if so it could just be starting up full loaded if the piston is stuck. you can try to hook your gauges to the end of the comp. where the piston is.( there should be a Schrader port already there) and the other side to the suction line after the comp. when it starts open both ports on your gauges to equalize the pressure and see if your RLA goes down if so then you have a comp starting fully loaded
-
08-11-2012, 07:15 PM #20
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 868
-
04-29-2013, 09:24 AM #21
New Guest
- Join Date
- Jul 2012
- Posts
- 3
Okay. Here we go.
I replaced the compressor.
I am pulling a vacuum on the unit.
It will come down to 1200 microns and then.... It starts climbing up and up and eventually it quits reading. What is going on?
Why would it pull down to 1200 and then go back up??
I have flushed the unit several times with nitrogen and changed the oil in my vacuum pump but it still does it.
Any ideas???
-
04-29-2013, 09:54 AM #22The weak aren't destroyed by the strong.
The weak are destroyed by the under-estimated.
I know a famous song that ends in 'my nose'. The artist is dead. Know who?
-
04-29-2013, 12:38 PM #23
Sure sounds that it has a leak or your setup has a leak. Possibly still getting refrigerant vapor out too.
-
04-29-2013, 02:58 PM #24
Professional Member
- Join Date
- Mar 2005
- Location
- Indiana
- Posts
- 125
1200 microns seems to be the magic number. I can't count how many times I have gotten to that number and couldn't get it any lower. It has always been a small leak or usually moisture. I just keep breaking the vacuum with nitrogen and pulling it down again until I get it down to a good level.
-
05-11-2013, 04:44 PM #25
Regular Guest
- Join Date
- May 2011
- Location
- NC Foothills
- Posts
- 38
Hook your pump up with soft copper and make sure all connections are tight. Make sure you have fresh oil in the pump, you know the drill. If you don't have any oil in the separator and none on the ground it's got to be in the machine. If it hasn't drained back to the separator during the course of your compressor change its probably in the evaporator. RTAC = 134A. You are not going to get it pulled down if it has been open for much length of time due to the oil absorbing oil. Not as bad as a 410 machine but bad enough. If the machine runs at low load conditions for extended periods it could have pumped the oil out. I would be willing to bet you will find the machine oversized or a EXV issue when you do get it up. Also just for future knowledge a front seated discharge valve can present just like a locked compressor without tripping on high head pressure.
-
05-12-2013, 08:59 PM #26
Regular Guest
- Join Date
- Dec 2005
- Location
- Southern California
- Posts
- 76
I just wonder how much EXTRA oil will be added to get an oil level?


Reply With Quote