Results 1 to 13 of 15
    Malden Mass
    Testing a condenser
    Hello to all,
    I have a five ton Goodman R-22 condenser I pulled out and replaced with a new one last year for a customer.
    Problem: I took this unit out, stored it, but I didn't write down what was wrong with it. I did closed down the refrigerant shut off's. I don't know if it has a huge leak or a bad compressor.
    I wanted to run it to see what is wrong with it.
    I am thinking of connecting a copper loop (few feet long) between the suction and discharge lines, fill it first with nitrogen, check for leaks.
    If I find no leaks, I can run a temporary line voltage and see if the compressor will kick on.
    What do you guys thinks of my methodology?
    Jul 2012
    San Francisco Bay area
    Sounds good to me
    Virginia
    Quote Originally Posted by jdere View Post
    I would OHM out the windings of the compressor first to see if they are even within limits, before I went to any more trouble.
    Malden Mass
    that's a good idea rundawg. I have various size used compressors and I am thinking of getting the condenser working and maybe selling it to a relative on a budget.
    Urbandale IA. USA
    Only accept CASH, GOLD, or blood.....
    Those who dance, appear insane to those who do not hear the music.
    Those who believe, appear ignorant to those who do not know God.
    Nov 2007
    Mississippi
    Sounds good
    Massachusetts
    I think if you just run a wad of copper tubing out between the high and low sides you won't have to wonder about the compressor very long! Absent a metering device you'll just be shoving liquid right back into the suction side of the compressor. BANG. So much for that compressor.
    north suburbs of Chicago
    Can't it just be started for a sec with the valves shut down? It's really no different than what you are doing when you close the discharge valve to pump down a system.
    can't you pressure test it without the copper, just use your manifold and hoses.
    Nov 2011
    Michigan
    Just using your guages sounds like a good idea.
    Jul 2012
    North west Arkansas
    If the valves are closed, aren't the fittings isolated off, along with the open lines?
    Quote Originally Posted by texasgentleman2 View Post
    Yeah. I forgot he wanted to pressure test it. I thought he had pumped down the system and was wondering if the compressor worked.
    Jul 2005
    Boston/Cape Cod
    I learned a long time ago to try to never work for friends or relative's
    southshorejohn