07-29-2012, 12:55 PM #27
-
07-29-2012, 01:57 PM #28
Professional Member
- Join Date
- Mar 2008
- Posts
- 64
SP=82
DP=255
SL temp=65
LL temp=110
Still not completely happy with the results.
-
07-29-2012, 02:17 PM #29
8SC. Dirty coil maybe.
-
07-29-2012, 02:27 PM #30
Is this a heat pump? If so, measure the rise in temp of the lines across the reversing valve to make sure it is not leaking.
Where are you measuring the suction line temp? is this as close to the evap as possible. and measuring LL as close to condenser as possible?
-
07-29-2012, 05:49 PM #31
Professional Member
- Join Date
- Mar 2008
- Posts
- 64
No it is not a heat pump. I measured superheat at the outdoor unit and subcooling at the outdoor unit.
-
07-29-2012, 07:03 PM #32
-
07-29-2012, 07:35 PM #33
-
07-29-2012, 08:03 PM #34
Professional Member
- Join Date
- Mar 2008
- Posts
- 64
Yeah I should have taken it at the evap as it does run through the attic and it is 103 here as well.
-
07-29-2012, 08:13 PM #35
Get in the habit of measuring SL and LL temperatures at condensing unit and at evaporator. It will reveal lineset problems.
Aircraft Mechanical Accessories Technician. The Air Force changed the job title to Air Craft Environmental Systems Technician. But I've decided I'll always be a Mech Acc.
-
07-29-2012, 08:17 PM #36
Professional Member
- Join Date
- Mar 2008
- Posts
- 64
So what is the consensus on this unit? Even adding refrigerant having trouble getting to the 10 degree subcooling on this unit?
-
07-29-2012, 08:23 PM #37
-
07-29-2012, 08:24 PM #38Aircraft Mechanical Accessories Technician. The Air Force changed the job title to Air Craft Environmental Systems Technician. But I've decided I'll always be a Mech Acc.
-
07-29-2012, 08:28 PM #39
Professional Member
- Join Date
- Mar 2008
- Posts
- 64
The outdoor unit has superheat charging chart so I used my Fieldpiece HG3 to get a 12 target subcool. Tell me about LL temp - outdoor rule you referenced?