    Quote Originally Posted by daviddsims View Post
    Took another look today and sure enough it had a txv on the evaporator. I added a small amount of refrigerant to try and get to 10 degrees subcooling. Getting about a 15 degree split out of the evaporator.
    What are you readings now.
  2. #28
    West Monroe, LA
    SP=82
    DP=255
    SL temp=65
    LL temp=110
    Still not completely happy with the results.
  3. #29
    8SC. Dirty coil maybe.
  4. #30
    Oct 2010
    AZ
    Is this a heat pump? If so, measure the rise in temp of the lines across the reversing valve to make sure it is not leaking.
    Where are you measuring the suction line temp? is this as close to the evap as possible. and measuring LL as close to condenser as possible?
  5. #31
    West Monroe, LA
    No it is not a heat pump. I measured superheat at the outdoor unit and subcooling at the outdoor unit.
  6. #32
    Oct 2010
    AZ
    Superheat at the outdoor unit really doesn't tell you much. You should measure it as close to the evaporator as possible.
  7. #33
    Jul 2005
    Quote Originally Posted by dijit View Post
    Yep, there's quite a difference on mine. About a 6 rise in line temp from evap to compressor. Figuring in pressure drop that gives me about a 7 difference in SH. It's about 103 outside right now and my line set runs through the attic.
  8. #34
    West Monroe, LA
    Yeah I should have taken it at the evap as it does run through the attic and it is 103 here as well.
  9. #35
    Jul 2000
    NW IL.
    Get in the habit of measuring SL and LL temperatures at condensing unit and at evaporator. It will reveal lineset problems.
    Aircraft Mechanical Accessories Technician. The Air Force changed the job title to Air Craft Environmental Systems Technician. But I've decided I'll always be a Mech Acc.
  10. #36
    West Monroe, LA
    So what is the consensus on this unit? Even adding refrigerant having trouble getting to the 10 degree subcooling on this unit?
  11. #37
    Jul 2005
    You didn't add enough.
  12. #38
    Jul 2000
    NW IL.
    What is the LL approach temperature? Liquid Line temperature - Ambient temperature if it is pushing 10 degrees may be a dirty condenser coil. If coil is clean it may be non condensables.
  13. #39
    West Monroe, LA
    The outdoor unit has superheat charging chart so I used my Fieldpiece HG3 to get a 12 target subcool. Tell me about LL temp - outdoor rule you referenced?