    glycol in chilled water system

    Wondering if there is a rule of thumb on how much a system is derated when glycol is added to a system. Example per say 300 ton chiller with 30% glycol you actually get 225 tons due to the heat transfer characteristics of the glycol.

    thanks

  2. #2
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,456
    Post Likes
    Quote Originally Posted by pipefittermarks View Post
    Wondering if there is a rule of thumb on how much a system is derated when glycol is added to a system. Example per say 300 ton chiller with 30% glycol you actually get 225 tons due to the heat transfer characteristics of the glycol.

    thanks
    I don't know of any rule of thumb. But most manufactures have charts showing the capacity vs glycol %.

  3. #3
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    Depends if its Ethylene or Propylene
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  4. #4
    Join Date
    Aug 2011
    Location
    Chicago
    Posts
    64
    Post Likes
    My experience any thing over 20% is a problem if it was designed for straight water. Approach temperatures increase to where chiller will drop out on refrig temp or pressure while chilled set point not made. Real problem on small DX systems because less engineering seems to be involved. Larger Centrifugal installs chiller more likely to be designed for anti freeze mix

  5. #5
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    Quote Originally Posted by Jimmyhat 597 View Post
    My experience any thing over 20% is a problem if it was designed for straight water. Approach temperatures increase to where chiller will drop out on refrig temp or pressure while chilled set point not made. Real problem on small DX systems because less engineering seems to be involved. Larger Centrifugal installs chiller more likely to be designed for anti freeze mix
    That's a good point. A system designed for use with glycol might have a larger or different evaporator configuration. Larger chillers always get designed as a custom package.

  6. #6
    Join Date
    Dec 2010
    Location
    On a Peninsula in NE NC
    Posts
    1,904
    Post Likes
    the buiding coils need to be sized for glycol as well. You loose capacity all the way around as well as pump performance.
    It's hard to stop a Trane. but I have made one helluva living keeping them going.

  7. #7
    Join Date
    Feb 2007
    Location
    Helena, Montana
    Posts
    2,130
    Post Likes
    Quote Originally Posted by Southern Mech View Post
    the buiding coils need to be sized for glycol as well. You loose capacity all the way around as well as pump performance.
    Ah the pumps....
    Don't worry zombies are looking for brains, you're safe...

  8. #8
    Join Date
    Mar 2011
    Posts
    279
    Post Likes
    Quote Originally Posted by Healey Nut View Post
    Depends if its Ethylene or Propylene
    How do you tell the difference?

  9. #9
    Join Date
    Dec 2010
    Location
    On a Peninsula in NE NC
    Posts
    1,904
    Post Likes
    Quote Originally Posted by TheChillerMan View Post
    How do you tell the difference?
    Taste

  10. #10
    Join Date
    Mar 2003
    Posts
    7,400
    Post Likes
    depending upon the evaporator design, it can range in the 10-15% area with propylene. This doesnt account for the added horsepower requirement of the pump(s).

  11. #11
    Join Date
    Apr 2004
    Location
    Winnipeg,MB,Canada
    Posts
    112
    Post Likes

    Glycol in chillers

    You lose approximately 25% of your heat transfer rate in a 50/50 mix. You're gonna run lower suction pressure, or higher head pressure, equipment needs to be selected for expected fluid concentrations, for proper operation.

  12. #12
    Join Date
    Sep 2008
    Location
    Delaware
    Posts
    243
    Post Likes
    Bottom line is looking at the SYSTEM. If you add glycol to a closely sized system that was designed for water if could be trouble. The chiller. coils. pumps and concentration of glycol all need consideration.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •