Results 1 to 12 of 12
    Feb 2012
    Kansas
    glycol in chilled water system
    Wondering if there is a rule of thumb on how much a system is derated when glycol is added to a system. Example per say 300 ton chiller with 30% glycol you actually get 225 tons due to the heat transfer characteristics of the glycol.
    thanks
    Jun 2006
    New Jersey
    Quote Originally Posted by pipefittermarks View Post
    thanks
    I don't know of any rule of thumb. But most manufactures have charts showing the capacity vs glycol %.
    ottawa canada
    Depends if its Ethylene or Propylene
    Aug 2011
    Chicago
    My experience any thing over 20% is a problem if it was designed for straight water. Approach temperatures increase to where chiller will drop out on refrig temp or pressure while chilled set point not made. Real problem on small DX systems because less engineering seems to be involved. Larger Centrifugal installs chiller more likely to be designed for anti freeze mix
    Saint Joseph, MI
    Quote Originally Posted by Jimmyhat 597 View Post
    That's a good point. A system designed for use with glycol might have a larger or different evaporator configuration. Larger chillers always get designed as a custom package.
    Dec 2010
    On a Peninsula in NE NC
    the buiding coils need to be sized for glycol as well. You loose capacity all the way around as well as pump performance.
    It's hard to stop a Trane. but I have made one helluva living keeping them going.
    Feb 2007
    Helena, Montana
    Quote Originally Posted by Southern Mech View Post
    Ah the pumps....
    Don't worry zombies are looking for brains, you're safe...
    Mar 2011
    Quote Originally Posted by Healey Nut View Post
    How do you tell the difference?
    Dec 2010
    Quote Originally Posted by TheChillerMan View Post
    Taste
    depending upon the evaporator design, it can range in the 10-15% area with propylene. This doesnt account for the added horsepower requirement of the pump(s).
    Winnipeg,MB,Canada
    Glycol in chillers
    You lose approximately 25% of your heat transfer rate in a 50/50 mix. You're gonna run lower suction pressure, or higher head pressure, equipment needs to be selected for expected fluid concentrations, for proper operation.
    Delaware
    Bottom line is looking at the SYSTEM. If you add glycol to a closely sized system that was designed for water if could be trouble. The chiller. coils. pumps and concentration of glycol all need consideration.