Results 1 to 4 of 4

Thread: Combo sensors

  1. #1
    Join Date
    Feb 2008
    Posts
    225
    Post Likes

    Combo sensors

    Anyone know of a temp/humidity/diff pressure combo sensor or meter
    or panel available?

    I have a operating room that I need to control all 3 conditions.

  2. #2
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,306
    Post Likes
    You could do accurate differential witgh a Dwyer magnahelic transmitter.

    Humidity and space temp should be easy enough to find

  3. #3
    Join Date
    Jul 2012
    Location
    Northern NY
    Posts
    121
    Post Likes
    I've done many of these projects and never had an combo sensor. I place a Setra (Typically a 265) above the ceiling or in the hallway for DP and a Setra Temp/RH sensor on the wall in the space.

    If you need to display the values on a panel in the OR I usually use a little LCD (many vendors) and use 4-20mA and place both the panel and the display on the sensor loop so they both see the same signal. No chance of someone accidentally commanding and output and messing up the display, etc.

    -Jeremy

  4. #4
    Join Date
    Nov 2007
    Location
    Sacramento, CA
    Posts
    63
    Post Likes
    I have never seen this type of combination.

    Easy to find a Temp/RH/Co2 combination from various vendors.

    We typically use Veris for Differential Pressure because it has a LCD display and they are easy to setup along with a 0-10vdc output.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.