Results 1 to 9 of 9
  1. #1
    Join Date
    Jul 2012
    Posts
    3
    Post Likes

    ytk6d5f2 need help

    to manually turn on purge pump set for 30 per hr but hasnt run

  2. #2
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,044
    Post Likes
    Quote Originally Posted by ckcraven View Post
    to manually turn on purge pump set for 30 per hr but hasnt run
    hasn't purged or hasn't run? is the chiller running?
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  3. #3
    Join Date
    Jul 2012
    Posts
    3
    Post Likes
    Thread Starter
    hasnt purged, chiller is running

  4. #4
    Join Date
    Jan 2011
    Posts
    1,582
    Post Likes
    Please describe the problem.

    You cannot "turn on" a York purge. Setting the "number" to 30 is a setting to show an alarm if the purge count reaches 30 in one hour (after the first hour of chiller runtime). A York turboguard purge works only when the chiller is running.

    Is this a single line panel?

  5. #5
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,044
    Post Likes
    Quote Originally Posted by ckcraven View Post
    hasnt purged, chiller is running
    perhaps there isn't any air in the chiller to be removed...that would be a good thing.
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  6. #6
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,623
    Post Likes
    Quote Originally Posted by ckcraven View Post
    hasnt purged, chiller is running
    need help, someone that knows

  7. #7
    Join Date
    Jul 2012
    Posts
    3
    Post Likes
    Thread Starter
    that would be good if there is no air, but man that thing can really do some surging at times

  8. #8
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    3,175
    Post Likes
    Air is not the only thing that can cause surging.

  9. #9
    Join Date
    Aug 2012
    Location
    Tijuana, Mexico
    Posts
    18
    Post Likes
    The purge pump has to be working when the chiller is in operation, when you start it check the purge pressure max. 90 psia. and then purges.