ytk6d5f2 need help
to manually turn on purge pump set for 30 per hr but hasnt run
-
 Originally Posted by ckcraven
to manually turn on purge pump set for 30 per hr but hasnt run
hasn't purged or hasn't run? is the chiller running?
Don't step on my favorite part of the Constitution just to point out your favorite part.
Political Correctness is forced on you because you have forgotten decency.
-
hasnt purged, chiller is running
-
Please describe the problem.
You cannot "turn on" a York purge. Setting the "number" to 30 is a setting to show an alarm if the purge count reaches 30 in one hour (after the first hour of chiller runtime). A York turboguard purge works only when the chiller is running.
Is this a single line panel?
-
 Originally Posted by ckcraven
hasnt purged, chiller is running
perhaps there isn't any air in the chiller to be removed...that would be a good thing.
Don't step on my favorite part of the Constitution just to point out your favorite part.
Political Correctness is forced on you because you have forgotten decency.
-
 Originally Posted by ckcraven
hasnt purged, chiller is running
need help, someone that knows
-
that would be good if there is no air, but man that thing can really do some surging at times
-
Air is not the only thing that can cause surging.
-
The purge pump has to be working when the chiller is in operation, when you start it check the purge pressure max. 90 psia. and then purges.