    I think I would have a look at the txv also. Some come adjustable and if someone has already been in the unit they may have played around with the adjustment.

  2. #15
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    If your freeze time is max and you have small ice think water first then refrigeration. If your freeze time is normal or short and small ice think board or float. I suspect you have more then one issue here. The high head could be the cause of small ice, if you have max freeze time, but is only a symptom of the actual problem. That being said if what you posted earlier, clean coil etc, nothing wrong with pulling charge replacing drier and weighing in charge the have a solid base to move forward from.

  3. #16
    Join Date
    Apr 2011
    Location
    Yooper-ville, Michigan
    Posts
    22
    Quote Originally Posted by Tommy knocker View Post
    Check defrost time. If evap is flaking it may not release the ice properly and you ice is being melted away before release. Regardless if the evap is flaking that's the #1 issue. Those flakes are going out with the ice and being consumed by customers. Good luck

    Just to let you know (original poster), the defrost time is the harvest cycle on an i/m. I only say this because you said that you haven't worked on many.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event