Page 2 of 2 FirstFirst 12
Results 14 to 18 of 18
  1. #14
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    9,035
    Post Likes
    Quote Originally Posted by Six View Post
    Its about Trane split system or supposed to be.

    Any input on the photo ?
    Do you have model number?

    Maybe the installers guide will shed some light.
    Instead of learning the tricks of the trade, learn the trade.

  2. #15
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,307
    Post Likes
    Thread Starter
    It was a weird service call. Its one of our customers that owns a bunch of Hotels and strip centers.

    This is a new Hotel.

    Dispatcher sent me out there for a water leak.

    When I showed up it was a block of Ice. Turned the fan on and let it thaw out. Took the panels off and two guys walked in and said it was warranty and they were the guys that installed it.

    Ok. Called the owner and he said he would call me back if they couldnt figure it out.

    Never had a chance to even get gauges on it or any information.

    That pan almost completley blocks off one side of the coil. Hack made a good point but couldn't control himself so the thread devolved from there.

    Im still curious though.

  3. #16
    Join Date
    Jul 2012
    Location
    Southwest
    Posts
    114
    Post Likes
    I have been all over Trane splits lately, and all the ones I look at have freeze protection on the coils. Almost every single one has required a leak repair that I have come across. These are less than 10 year old Trane splits. Also, I have changed quite a few txvs on them, the ones that thread on.

  4. #17
    Join Date
    Feb 2006
    Location
    FL
    Posts
    571
    Post Likes
    For upflow, the install manual tells you to remove that pan, and remove the horizontal baffle and replace with the narrow one. The narrow one is on top of baffle already screwed to the top of the coil. It reduces turbulence and such but if you leave it on, like hack said, if your unit is horizontal, doesnt make that much of a diff. i wouldnt think.

  5. #18
    Join Date
    Mar 2011
    Posts
    1,075
    Post Likes
    You can remove the horizontal pan and gain some efficiency, also the metal block off plate on top of the coil can be swapped with the supplied plate which is less restrictive.

    Neither of those items will cause a coil to ice. More likely a refrigerant leak on the evaporator, with the paper thin tubes they are using, an then they rifle the inside for even less wall thickness. Dirty coil and or poor supply duct work are two common ones also.