    I would love to know the Carrier model numbers for these units.

    Let's assume these are standard RTU's that are just running the OA dampers 100%......you're getting a 23 degree split and your maintaining a 79 degree space temp. What kinda of ambient temps are we talking?

    Your manager said six years ago they were able to maintain mid 70's during the day and your at high 70's.......are you still at the same airflow and discharge temperatures. A slight change in either will cause a 3-5 degree change as you stated.

  2. #15
    Quote Originally Posted by ascj View Post
    I would love to know the Carrier model numbers for these units.

    Let's assume these are standard RTU's that are just running the OA dampers 100%......you're getting a 23 degree split and your maintaining a 79 degree space temp. What kinda of ambient temps are we talking?

    Your manager said six years ago they were able to maintain mid 70's during the day and your at high 70's.......are you still at the same airflow and discharge temperatures. A slight change in either will cause a 3-5 degree change as you stated.
    The units are Carrier Model 50TM--016--511QA's

  3. #16
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,337
    Quote Originally Posted by FloridaWolf View Post
    The units are Carrier Model 50TM--016--511QA's
    Good luck.

    Common case of wrong equipment for the application.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event