Thread: "ganging" pneumatic t-stats

  1. #1
    Join Date
    Dec 2007
    Location
    Soudern Kaliphonistan
    Posts
    298
    Post Likes

    "ganging" pneumatic t-stats

    I am about to open up a bunch of office space into one large area, as opposed to smaller rooms and offices. This 3000 sf area is served by 8 or 9 VAV's...and I want to be sure that the t-stats dont compete with each other.

    If I were to connect all of the "signal" outputs together, would this then "average" the signal and make all of the VAV's act identically? (assuming calibration and air valve size are the same).

    No budget for DDC, even tho I pitched it as hard as I could....


    thanks all.

  2. #2
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,312
    Post Likes
    No it wouldn't .

    Your'e assuming quite a bit here and I dont understand your reasoning. With one or 8 stats you should reach a sustained average temp. with specific areas responding to accute heat loads.

    Chances are the calibration from one stat to the next is off a little or a bunch not too mention you most likely have velocity reset controlers that take an input from a single stat to provide minimum and maximum CFM per VAV.

    It would be a mess even with one stat serving all the VAVs which you wouldn't have enough of a signal. ( volume ) to accomplish.

    Competing VAVs shouldn't be an issue if the Stats are located in their respective areas.

    There is nothing wrong with a pnuematics set up as long as it is maintained correctly.

  3. #3
    Join Date
    Apr 2007
    Location
    North Texas
    Posts
    1,144
    Post Likes
    I did it with two vav's years ago. Two small offices now turned into one. As far as I know it's still like that and it worked well at the time. There was only one hole in the marble for one stat so that's what they got.
    "It's not that I'm smart, it's that I stay with the problem longer”
    Albert Einstein

  4. #4
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,312
    Post Likes
    MAYBE with two VAVs you coud get away with it.

    One of the problems you run into is you lose signal volume with that many actators AND your reset controlers will act up. Its one of the reasons why you see pilot positioners on large actuators.

    Each velocity reset is set up for that VAV when commisioned. A signal on the other aide of the room isn't going to control that VAV accurately.

    I would rather toss the thermostats up into the grid ro sense plenum temp rather than jerry rig them.

  5. #5
    Join Date
    Jul 2001
    Location
    Canada
    Posts
    1,913
    Post Likes
    The signal to the actuator is from the velocity controller not the tstat so your loss of signal volume is a bit ?able.

    Have setup plenty of large sq footage areas in this manner for TEMPORARY control after the areas were gutted and real estate company was trying to lease it and only wanted to worry about 1 tstat for them to fiddle with.

    Had a few they wanted to keep like this after the space was leased and occupied , but too my problems and rezoned to suit tenants.

  6. #6
    Join Date
    Jun 2009
    Location
    StL, MO
    Posts
    730
    Post Likes
    If you connect multiple themostat branch lines together the result is a low signal select. The 'stat with the lowest pressure output will bleed off the other thermostats.

    You can connect about as many volume controllers as you want to a single thermostat. I've seen as many as twelve. The reason this works is that the volume control "T" connection is a dead end; typically a small diaphragm inside the controller. You can prove this to yourself with a squeeze bulb.
    UA LU 562

  7. #7
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,312
    Post Likes
    Quote Originally Posted by Control Man View Post
    The signal to the actuator is from the velocity controller not the tstat so your loss of signal volume is a bit ?able.

    Have setup plenty of large sq footage areas in this manner for TEMPORARY control after the areas were gutted and real estate company was trying to lease it and only wanted to worry about 1 tstat for them to fiddle with.

    Had a few they wanted to keep like this after the space was leased and occupied , but too my problems and rezoned to suit tenants.
    Not having reset velocity controlers means you would have a loss of signal volume. That is one branch output to 9 VAVs would be the same as that branch to a huge actuator.

    Without a pilot positioner your'e dead in the water. I had a building with old McQuays with variable inlet guide vanes and big actuators to drive them.


    Having velocity controllers means that velocity reset between min and max settings is possible regardless of setpoint.

    Either way I dont see it working and imagine cold and hot spots throughout the space.

    I've come behind guys who did stuff like that, usually building " engineers " and wish they would have just left it alone. It's hack service work in my book.

  8. #8
    Join Date
    Sep 2006
    Location
    Anchorage Alaska
    Posts
    641
    Post Likes

    Capacity relays

    https://estore.industrialcontrolsonl...RP970A1008.pdf

    I've controlled about 8 vav boxes with reheat with one tsta and a capacity relay.
    Law Of The Thermostat: He who has the thermostat wins!!!!!

  9. #9
    Join Date
    Jul 2001
    Location
    Canada
    Posts
    1,913
    Post Likes
    Well 6 seems your hung up on pilot positioners , so I will bow out on this thread , my 38 years and thousands of VAV box installs , repairs , service and I can count the # of piot positioners on a VAV on 1 hand.

    No need for a long reply , sorry I posted in the 1st place.

  10. #10
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,312
    Post Likes
    Quote Originally Posted by Control Man View Post
    Well 6 seems your hung up on pilot positioners , so I will bow out on this thread , my 38 years and thousands of VAV box installs , repairs , service and I can count the # of piot positioners on a VAV on 1 hand.

    No need for a long reply , sorry I posted in the 1st place.
    I'm not trying to argue with you Control man or tell the Op to use pilot positioners on a VAV.

    I brought them up to more or less illustrate my point about losing branch volume when T-ing off to too many actuators.

    If youv'e done it and it's worked then thats great, I just dont think its a effective way to control 9 VAVs over a 3000 sq foot open space.

    I've got a building thats 3 floors of open space with cubicles and I'm not running into the problem the OP was concerned with in his first post.

    ( t-stats ) fighting each other. As long as they remain calibrated it the floors space temp seems to maintain a even and confortable temp.

    Also one stat for nine Vavs when you have exterior pocket heaters just doesnt sound like it would work effectivley.

  11. #11
    Join Date
    Dec 2007
    Location
    Soudern Kaliphonistan
    Posts
    298
    Post Likes
    Thread Starter

    thanks for all the input

    this might be a good time to begin the painful conversion to DDC, eh?

    Buildings are 60 years old, and I think a reducting with new VAV's is the proper way to renovate this space. Hope I can convince the bean counters!


  12. #12
    Join Date
    Nov 2001
    Location
    Seattle, WA
    Posts
    8,352
    Post Likes
    If I understand the sequence right it's best, IMO, to limit the number of TStat's in the common area and then run the signals from the used TStats into pilot one to one relays where the strength of the branch signal only signal the pilot realay, which uses main air for power and the TStat signal for a signal only. So the power comes from the pilot relay and not form the TStat.

    Not saying this right but this will allow contol of many devices by the use of only one TStat. Hope this makes sense. Control man can clarify what I'm saying if it does not make sense.
    "The American Republic will endure until the day Congress discovers it can bribe the public with the public's own money.
    - Alexis de Toqueville, 1835

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •