Results 14 to 26 of 33
Thread: a-coil wont get cold enough
-
07-26-2012, 07:09 PM #14
I've made some more notes in red. I was in a hurry earlier to go to dinner with my family.
I also highlighted what I believe to be the error in your logic in blue. Could you please explain to me why you believe that a compressor problem, with what you claim to be "perfect pressures" could be causing your problem?
The compressor is pumping, you needn't ask more from it at this point in time.
As requested, please take the requested readings and post back. We'll explain what the problem is and WHY we know it to be the problem from the information that you haven't yet provided.
-
07-26-2012, 07:18 PM #15
So Blowing a Ton of Hot air across your coil wouldn't cause it not to be wet? I think you better run the unit close the liquid line valve and see if your gauge Retards.
Or just listen to JP advice cause he knows his Refer
We need more info to help you
-
07-26-2012, 10:12 PM #16
I will say air flow is MOST DEFINITELY something to check.
Had an almost same situation today, low TD, low pressures, warm coil, SH & SC off and they wanted on one of our maintenance policies.
Mind you, this unit was installed as a package with a furnace in 1995 by others. We have serviced the furnace since 2002, but only replace the capacitor in the outdoor unit and nothing else done according to the service sticker.
Well it was a 75K furnace with a 1.5T a/c with blower tap for cooling on high.
I found an old invoice with a reading of 11555 CFM, 50/120 PSIG, 74° AMB and a
16° TD. This was also after he added a LB of refrig because he replaced the core due to a leak( maybe low pressures due to improper, too much, airflow?).
Duct work is spotty at best.
Lowered to heat tap, which was 752 CFM, lowest possible, got a 16° TD, but it is, was and will always be WRONG!!!
So YES airflow matters!!!!!!!If Guns Kill People, Do Pencils Misspell Words?
http://www.youtube.com/watch?feature...&v=2kX_3y3u5Uo
http://www.youtube.com/watch?v=JVAhr4hZDJE
http://www.youtube.com/watch?v=-TC2xTCb_GU
-
07-26-2012, 10:29 PM #17
This is just a wild guess from a new student. I am thinking oversized orifice because of low superheat with high suction side pressures.

JASON sent this from his DUMB-PHONE
-
07-26-2012, 10:30 PM #18
Professional Member*
- Join Date
- Nov 2009
- Location
- Kansas City
- Posts
- 114
Definitely need all your data:: return dry bulb, return wetbulb, supply temp, outside ambient, low pressure, high pressure, liquid line temp, suction line temp, condenser saturation temp, and evap saturation temp, with all those numbers you can tell exactly what is wrong, no ifs ands or butts. Science doesn't lie
-
07-26-2012, 10:30 PM #19
-
07-26-2012, 10:34 PM #20
give the guys want they want.... superheat wet bulb dry bulb and you will get help..... no info we cant help.... and 80 suction is not really all that normal
it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair
-
07-26-2012, 10:34 PM #21
-
07-26-2012, 10:39 PM #22
-
07-26-2012, 10:43 PM #23
-
07-26-2012, 10:47 PM #24
-
07-26-2012, 11:08 PM #25
One of these days I am going to correctly diagnose one of these internet service calls.

Jp, is SST suction superheat temp and SCT subcool temp ?
JASON sent this from his DUMB-PHONE
-
07-27-2012, 05:58 AM #26



Reply With Quote