    Matsu****a rotary compressor backspins

    I had a maintinence man call me and describe what sounded like a broken compressor. It's a First Co. hotel unit. The condenser was dirty and compressor was near max LRA. Rated for 6.6, running at 6.3. On shutdown, compressor had a wicked backspin, rattling and knocking for 15-20 seconds. I figured "this is easy, dirty condenser coil." After cleaning, it runs cooler and RLA dropped to a proper 5.0. But the comp. still backspins loudly. I don't have operating pressures as this is a sealed system w/no access valves. Temp drops are about 16 degrees and the "touch" of the lines tells me it is properly charged. Operates properly except for the rattle. Do these small 1.5 ton units have a built in check valve to prevent this from happening?

  2. #2
    Join Date
    Mar 2010
    Location
    Kent, WA.
    Posts
    200
    Post Likes
    I had a 3/4 ton water source heat pump with a rotary compressor do this. It would work great but when it shut off the refrigerant head pressure would spin the comp backwards and it made quite the racket. Considering this was a bedroom unit in a closet of an apartment building i had to replace the unit. I believe the compressor might have a valve on the discharge and when its not sealing anymore consider it das kaput.

  3. #3
    Join Date
    Apr 2007
    Location
    Pa
    Posts
    774
    Post Likes
    check valve is bad. Instaleld a 50 ton carrier and the new compressor did this. Carrier ate that one and replaced the compressor and paid for the crane and all!

  4. #4
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,843
    Post Likes
    Quote Originally Posted by HvAckid82 View Post
    check valve is bad. Instaleld a 50 ton carrier and the new compressor did this. Carrier ate that one and replaced the compressor and paid for the crane and all!
    Was it a Copeland?

  5. #5
    Join Date
    Apr 2007
    Location
    Pa
    Posts
    774
    Post Likes
    No danfoss

  6. #6
    Join Date
    May 2010
    Location
    Oxford, UK
    Posts
    344
    Post Likes
    If its just the faulty internal check valve thats wrong with the compressor, an external one fitted in the discharge line can be worth considering.

  7. #7
    Join Date
    Nov 2005
    Location
    Madison WI
    Posts
    4
    Post Likes
    Thread Starter
    Thanks guys. I was fairly certain that was the problem but wanted confirmation. I think rotaries should be outlawed. Noisy and seem to be very fragile as far as talking abuse such as slugging. They must be very cheap to build.