    having low discharge superheat problems,the circuit will load to about 70% the dsh will drop and will unload. Checked all temp&pressure sensors. Need some help with this problem,

  2. #2
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,307
    Post Likes
    Low discharge superheat typically means your bringing back liquid to the compressor.

    In your case it's probably a bad sensor unless you can verify EXV operation isnt controlling superheat correctly.

  3. #3
    Join Date
    Feb 2003
    Location
    Wichita Ks
    Posts
    1,588
    Post Likes
    it is not uncommon for the exv to hang up during operation. pull each temp sensor and compare with an accurate thermometer, I will use a cup of water and see if it reads right. also check ball valve for oil skimmer line, if open all the way back it off about half.