Hi I agree. What I meant is a deeper coil give you better contact hence better for dehum. When you have a look the coil in an operating theater AHU you'll normally find it comes with 6 rows coil. Of course its with chilled water as well to bring down the off coil conditions n better dehum. (This is based on a hotter n more humid climate.) At the end of the day its depend on how much latent the coil need to meet. A residential situation its probably not that much of a problem if you r not talking a massive amounts of fresh air/moisture. Of course you still need to insulate your ductwork properly to lag the heat transfer n minimise chances of condensation. Sorry off topic a bit.
-
09-15-2012, 08:04 PM #15
Professional Member
- Join Date
- Sep 2012
- Posts
- 24
Hi I agree. What I meant is a deeper coil give you better contact hence better for dehum. When you have a look the coil in an operating theater AHU you'll normally find it comes with 6 rows coil. Of course its with chilled water as well to bring down the off coil conditions n better dehum. (This is based on a hotter n more humid climate.) At the end of the day its depend on how much latent the coil need to meet. A residential situation its probably not that much of a problem if you r not talking a massive amounts of fresh air/moisture. Of course you still need to insulate your ductwork properly to lag the heat transfer n minimise chances of condensation. Sorry off topic a bit.
-
09-15-2012, 11:26 PM #16
"Over sized ac to dehumidify " is not a good strategy. Reheat is not allowed in most energy codes. Air movement in the attic to help duct sweating??
Removing moisture is about cold coils and the length of the cooling cycle. You need a 45^F coil with a hour run time. The drain pan must drain well.
Sorry for being so blunt.
Regards TBBear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
Use +Merv 10 air filter. -Don't forget the "Golden Rule"
-
09-16-2012, 12:34 AM #17
Professional Member
- Join Date
- Sep 2012
- Posts
- 24
Absolutely right. I think I need to make it clear. I'm against oversizing equipment and add reheat. I also think its not much of problem in winter as long as insulation is properly done. I'm just saying a normal DX split does not give you the ability to actively control humidity. It only gives you temperature control. Venting the attic space will help in summer.
The latent capacity of the unit/coil provide you the dehum.
-
09-16-2012, 12:35 AM #18
Professional Member
- Join Date
- Sep 2012
- Posts
- 24
Absolutely right. I think I need to make it clear. I'm against oversizing equipment and add reheat. I also think its not much of problem in winter as long as insulation is properly done. I'm just saying a normal DX split does not give you the ability to actively control humidity. It only gives you temperature control. Venting the attic space will help in summer.
The latent capacity of the unit/coil provide you the dehum.
-