Thread: over amping blower assembly

  1. #1
    Join Date
    Jul 2007
    Location
    New Jersey
    Posts
    3,035
    Post Likes

    over amping blower assembly

    Carrier water cooled omnizone package unit
    model 50XCW16AAQG6AA0AA

    brand new install

    blower motor rated at 4.3FLA...pulling 9.1, tripping safety reset on contactor

    remove belt motor pulls 2.5 ?????

    motor had rust inside on shaft and around body

    called carrier...they sent new motor

    same exact result

    WTF????

    any ideas?
    “If I have seen further than others, it is by standing upon the shoulders of giants.” ~ Sir Isaac Newton


    I'm learning all the time, the tombstone will be my diploma!!!


    Did you ever stop to think, and forget to start again?

  2. #2
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    4,021
    Post Likes
    Shive correct? Voltage correct? Wired correct?

  3. #3
    Join Date
    Jul 2007
    Location
    New Jersey
    Posts
    3,035
    Post Likes
    Thread Starter
    Quote Originally Posted by KB Cool View Post
    Shive correct? Voltage correct? Wired correct?
    Supply Voltage concerns me a LIL...445v

    fan pulley also caught my attention...seems small...but its the standard from carrier..
    “If I have seen further than others, it is by standing upon the shoulders of giants.” ~ Sir Isaac Newton


    I'm learning all the time, the tombstone will be my diploma!!!


    Did you ever stop to think, and forget to start again?

  4. #4
    Join Date
    Nov 2001
    Location
    East Texas
    Posts
    1,221
    Post Likes
    Moving too much air ?

    Are the panels in place ?

  5. #5
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Are you saying that you have 445 on a 460 unit, or is it something else?

    A small motor sheave would not increase your draw. A small blower sheave would.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  6. #6
    Join Date
    Jul 2007
    Location
    New Jersey
    Posts
    3,035
    Post Likes
    Thread Starter
    Quote Originally Posted by timebuilder View Post
    Are you saying that you have 445 on a 460 unit, or is it something else?

    A small motor sheave would not increase your draw. A small blower sheave would.
    yes i have 445 on 460 unit
    “If I have seen further than others, it is by standing upon the shoulders of giants.” ~ Sir Isaac Newton


    I'm learning all the time, the tombstone will be my diploma!!!


    Did you ever stop to think, and forget to start again?

  7. #7
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Check to see if it's single phasing. Was the cover on when you took those amp readings?

  8. #8
    Join Date
    Oct 2007
    Location
    Broward County, FL.
    Posts
    675
    Post Likes
    Is the motor rpm correct? Did they send you a 3450 rpm instead of a 1725 rpm?

    Check your pulley ratio.

    As mentioned above recheck your wiring connections and make sure you don't have a dropped phase.
    I miss you mom and dad.

  9. #9
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,302
    Post Likes
    Your pecker head wiring is either wrong or not making a connection

    Don't assume because it is nutted that it is making a connection

  10. #10
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Check amps on all 3 legs.

    i don't think that having the panels off would cause that kind of overload.

    I'm thinking single phase or wrong motor like someone else said.



  11. #11
    Join Date
    Mar 2010
    Location
    Kent, WA.
    Posts
    218
    Post Likes
    The low voltage concerns me. A 460 unit actually is around 480. Now if you have a motor designed to run at 480v and you have 445 your amp draw will increase at the motor to maintain the design rpm. You can play with some fan laws to change sheaves to get your amps down to nameplate but then your cfm would suffer. I would look into the low incoming voltage.

  12. #12
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by Tommy1010 View Post
    yes i have 445 on 460 unit
    The book says that 414 is the lowest allowable voltage.

  13. #13
    Join Date
    Feb 2011
    Location
    Orange County, in a Galaxy far far away...
    Posts
    282
    Post Likes
    Check motor windings, check connections and fuses at disco box. Also take your infrared gun and check heat differential across line and load terminals in disco box. Generally anything above 3-4 deg is bad. I would also check continuity in all wires involved with blower. It's behaving like its wrong voltage or single phasingq. Dig in and find the answer!
    You cannot cheat an honest man. But that doesn't stop people trying!

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •