Thread: over amping blower assembly
-
07-24-2012, 10:56 AM #1
Professional Member
- Join Date
- Jul 2007
- Location
- New Jersey
- Posts
- 3,031
over amping blower assembly
Carrier water cooled omnizone package unit
model 50XCW16AAQG6AA0AA
brand new install
blower motor rated at 4.3FLA...pulling 9.1, tripping safety reset on contactor
remove belt motor pulls 2.5 ?????
motor had rust inside on shaft and around body
called carrier...they sent new motor
same exact result
WTF????
any ideas?“If I have seen further than others, it is by standing upon the shoulders of giants.” ~ Sir Isaac Newton
I'm learning all the time, the tombstone will be my diploma!!!
Did you ever stop to think, and forget to start again?
-
07-24-2012, 11:28 AM #2
Shive correct? Voltage correct? Wired correct?
-
07-24-2012, 11:41 AM #3
Professional Member
- Join Date
- Jul 2007
- Location
- New Jersey
- Posts
- 3,031
“If I have seen further than others, it is by standing upon the shoulders of giants.” ~ Sir Isaac Newton
I'm learning all the time, the tombstone will be my diploma!!!
Did you ever stop to think, and forget to start again?
-
07-24-2012, 11:53 AM #4
Professional Member*
- Join Date
- Nov 2001
- Location
- East Texas
- Posts
- 832
Moving too much air ?
Are the panels in place ?
-
07-24-2012, 11:57 AM #5
Are you saying that you have 445 on a 460 unit, or is it something else?
A small motor sheave would not increase your draw. A small blower sheave would.[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
07-24-2012, 12:50 PM #6
Professional Member
- Join Date
- Jul 2007
- Location
- New Jersey
- Posts
- 3,031
-
07-24-2012, 01:13 PM #7
Check to see if it's single phasing. Was the cover on when you took those amp readings?
-
07-24-2012, 01:42 PM #8
Is the motor rpm correct? Did they send you a 3450 rpm instead of a 1725 rpm?
Check your pulley ratio.
As mentioned above recheck your wiring connections and make sure you don't have a dropped phase.I miss you mom and dad.
-
07-24-2012, 04:48 PM #9
Your pecker head wiring is either wrong or not making a connection

Don't assume because it is nutted that it is making a connection
-
07-24-2012, 05:31 PM #10
Check amps on all 3 legs.
i don't think that having the panels off would cause that kind of overload.
I'm thinking single phase or wrong motor like someone else said.
-
07-24-2012, 09:15 PM #11
Professional Member
- Join Date
- Mar 2010
- Location
- Kent, WA.
- Posts
- 154
The low voltage concerns me. A 460 unit actually is around 480. Now if you have a motor designed to run at 480v and you have 445 your amp draw will increase at the motor to maintain the design rpm. You can play with some fan laws to change sheaves to get your amps down to nameplate but then your cfm would suffer. I would look into the low incoming voltage.
Experience
Is what you get when you didn't get what you wanted.
A positive attidude will not solve all your problems, but it will annoy enough people to make it worthwhile.
-
07-24-2012, 11:10 PM #12
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,512
-
07-25-2012, 12:20 AM #13
Professional Member
- Join Date
- Feb 2011
- Location
- Orange County, in a Galaxy far far away...
- Posts
- 233
Check motor windings, check connections and fuses at disco box. Also take your infrared gun and check heat differential across line and load terminals in disco box. Generally anything above 3-4 deg is bad. I would also check continuity in all wires involved with blower. It's behaving like its wrong voltage or single phasingq. Dig in and find the answer!
You cannot cheat an honest man. But that doesn't stop people trying!