Results 1 to 13 of 13
    New Jersey
    over amping blower assembly
    Carrier water cooled omnizone package unit
    model 50XCW16AAQG6AA0AA
    brand new install
    blower motor rated at 4.3FLA...pulling 9.1, tripping safety reset on contactor
    remove belt motor pulls 2.5 ?????
    motor had rust inside on shaft and around body
    called carrier...they sent new motor
    same exact result
    WTF????
    any ideas?
    “If I have seen further than others, it is by standing upon the shoulders of giants.” ~ Sir Isaac Newton
    I'm learning all the time, the tombstone will be my diploma!!!
    Did you ever stop to think, and forget to start again?
    Phoenix,AZ
    Shive correct? Voltage correct? Wired correct?
    New Jersey
    Quote Originally Posted by KB Cool View Post
    Supply Voltage concerns me a LIL...445v
    fan pulley also caught my attention...seems small...but its the standard from carrier..
    Nov 2001
    East Texas
    Moving too much air ?
    Are the panels in place ?
    Southeastern Pa
    Are you saying that you have 445 on a 460 unit, or is it something else?
    A small motor sheave would not increase your draw. A small blower sheave would.
    New Jersey
    Quote Originally Posted by timebuilder View Post
    yes i have 445 on 460 unit
    Jul 2005
    Check to see if it's single phasing. Was the cover on when you took those amp readings?
    Oct 2007
    Miami, FL.
    Is the motor rpm correct? Did they send you a 3450 rpm instead of a 1725 rpm?
    Check your pulley ratio.
    As mentioned above recheck your wiring connections and make sure you don't have a dropped phase.
    I miss you mom and dad.
    Mount Airy, MD
    Your pecker head wiring is either wrong or not making a connection
    Don't assume because it is nutted that it is making a connection
    Check amps on all 3 legs.
    i don't think that having the panels off would cause that kind of overload.
    I'm thinking single phase or wrong motor like someone else said.
    Mar 2010
    Kent, WA.
    The low voltage concerns me. A 460 unit actually is around 480. Now if you have a motor designed to run at 480v and you have 445 your amp draw will increase at the motor to maintain the design rpm. You can play with some fan laws to change sheaves to get your amps down to nameplate but then your cfm would suffer. I would look into the low incoming voltage.
    Experience
    Is what you get when you didn't get what you wanted.
    A positive attidude will not solve all your problems, but it will annoy enough people to make it worthwhile.
    Dallas ,Texas
    Quote Originally Posted by Tommy1010 View Post
    The book says that 414 is the lowest allowable voltage.
    UA 100
    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
    Feb 2011
    Orange County, in a Galaxy far far away...
    Check motor windings, check connections and fuses at disco box. Also take your infrared gun and check heat differential across line and load terminals in disco box. Generally anything above 3-4 deg is bad. I would also check continuity in all wires involved with blower. It's behaving like its wrong voltage or single phasingq. Dig in and find the answer!
    You cannot cheat an honest man. But that doesn't stop people trying!