Page 2 of 2 FirstFirst 12
Results 14 to 17 of 17

Thread: carrier clo

  1. #14
    Previous post is right probably bad cfm works in morning late afternoon gets hot trip out. Check case temp to see how hot its getting.

  2. #15
    Join Date
    Mar 2010
    Location
    plano,IL
    Posts
    28
    Not sure if anyone is following this post anymore, but I returned to the store the next morning, 7-24 to find the store at 75 and very comfortable.

    Checked the high pressure switches I installed, non tripped. Cycled on and off a few times just to test everything and as I was about to throw in the towel the condensor fans start winding down, then off, followed by comps tripping on HPS.

    I found the relay for the CFMS with a intermittently open contact. 24v at coil leg 1 closed leg 2 open.... replaced and tested again and all is well. odd how the previous time the contacts " reset" themselves and both CFMS were running at full speed.

    Right place at the right time sure is helpful

    Thanks to everyone for the info on the CLOs and the other input

  3. #16
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,080
    Nice find. Thanks for the info.



    Sent from my iPad using Tapatalk HD
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  4. #17
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    17,919
    Good job!!!!
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event