Results 1 to 13 of 28
    Jun 2012
    Batonrouge
    carrier rtu on walgreens contactor issues
    I have ran into few carrier units where the contractors are not sucking in all the way. I changed the transformer and a few months later I'm here again facing the issue. Voltage is 208 and I do not have a voltage drop on my primary or secondary. A couple other techs are finding the same problem with their Carrier units. These are on Walgreen, any help would be great.
    Apr 2012
    Paper Street Soap Company
    Wire to conventional stats or a EMS system ?
    You can isolate the stats and just operate it from the control panel to see if its in the ubit or in the stat wiring.
    Jun 2012
    Batonrouge
    Ems system. It only happens every once in a while if I reset the unit it will run fine for about a month or two.
    East of big city prices.
    Wow with the Carrier model number you didn't provide the possibilities are endless.
    NH
    If you push the contractor in does it stay running?????
    If so the unit may have been locked out. Pushing the contactor in will reset it or turning the unit off and on will reset it.
    Model number would help.
    Apr 2004
    Maryland
    What is your control voltage at the contactor when it is not pulling in? I have seen Carrier units locked out through the CLO board and have 16-17 volts at the contactor. When you push it in the contactor stays. 17 volts is not enough to pull in the contactor but when you push it in it will hold it closed.
    I would be checking your safeties closely. Maybe you have a condenser motor overheating or an intermittent blower.
    Jul 2011
    Lehigh Valley, PA
    You have a dirty low voltage connection somewhere. Low voltage will show 24v when tested with your vom but once put to a load will drop and create issues you state.
    Apr 2012
    Its has something to do with the EMS inputs.
    All the Carrier package RTUs Ive worked on and the only time Ive had anything remotely simar was when they were wired through a NOVAR system.
    What is the voltage & tolerance of the ems controllers? All inputs should be isolated in a perfect world. One chain of accounts i do the ems folks don't want more than 24 for control & they prefer 22. This utilizes system xfmrs & has been causing issues as of late. Especially in L serious lennox stuff which recognizes the higher input for safeties being closed & such. Lately I've been adding step down xfmrs off the units xfmr secondary just keeping their controllers at the lower scale. What a fkn pain in the a$$ on a carrier with no room in the control compartment as it is
    Pa
    Standard units up to 15 tons or so, our expierence, it is always the time delay
    Quote Originally Posted by HvAckid82 View Post
    For me with carriers I've been finding economizer problems causing most of my control issues when units are tapped right on the xfmr
    Jun 2012
    Batonrouge
    If I push the contactor in it will hold it in. If I shut the unit off and kick it back on it works fine. Last time this happened I changed the transformer from 40 va to 75. It worked fine for about a month. I know im going to have to go back. I checked the voltage at the transformer and I had 25 volts. Sorry no model num fellas. I'll get it next time.
    Jul 2012
    portland
    is your common grounded??