    wtf

    3 comp rack med temp Oil leak on flare fitting going into oil regulator repflare. All good x 2 days. Bam same problem, change copper line and new flare nut. All good x 2 days and it happend again. Im going crazy....

  2. #2
    Join Date
    Jun 2012
    Location
    Wisconsin
    Posts
    118
    This may seem like a dumb question, but are you burring out the tubing before you make a flare?

  3. #3
    Join Date
    Nov 2010
    Location
    MN
    Posts
    146
    Using oil on flare, before and after flaring? Try a new nut.

  4. #4
    Join Date
    Nov 2005
    Posts
    386
    Three things...

    1: Too much elbow greese when tighting those flares. lol
    2: Vibration issue, which i doubt cause it would've been noticable
    3: Same flare nut used, maybe bad flare nut.
    bonus one: forgot to tighten flare nut !!! LOL when ya tired things happen.

  5. #5
    Join Date
    May 2009
    Location
    The Pas, Manitoba Canada
    Posts
    212
    Drop of loctite? Would eliminate flarenut loosening.

  6. #6
    Join Date
    Jul 2012
    Location
    Southwest
    Posts
    114
    Go buy a factory flare with an extension and nut on it already and braze in the connection.

  7. #7
    Join Date
    Apr 2010
    Location
    Richmond, Virginia
    Posts
    311
    Check for bad compressor on that rack!

  8. #8
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    3,179
    how long is this line ? Make a longer one and coil it in a couple of circles to absorb vibration.