    Jul 2012
    venice ca
    Supply/Retrn temp question- prtble A/C
    i have this apc ac. do these numbers look acceptable?
    thank u in advance
    Sep 2010
    Western, MO
    Are you in the desert?
    jim
    Common sense isn't very common anymore.
    Jul 2012
    venice ca
    im in los angeles
    Saint Joseph, MI
    Hard to say without knowing the design airflow/ton. But if that remote RH and temperatuer is correct, you should have a dry coil. I think protables are usually only 350CFM/ton or less, so I'd say a 16F delta T with humidity that low isn't very good.
    Jul 2012
    venice ca
    thanks for that. ive done some research and have the factory service manual. its a 2speed/13000btu unit. what i found odd is the cfm in the specs, low=450 and high=650
    with the unit being a little over 1ton, 650cfm is way too high for job. BTW the coil is NOT dry, it condensates and a pump gets it outa there. i was getting 20f delta T on the low setting and 12-13f on the high setting. its a quality unit/ its got ebmpapst impellors for the condensor and the evaporator. so what i did is run an extra 10uf cap in parallel w/the low speed cap. that increased the cfm on the low setting and got me 16f.
    Jul 2012
    venice ca
    the temp seems right but the humidy is off. its working pretty good right now.