+ Reply to Thread
Results 1 to 7 of 7

Thread: Checking blower motor

  1. #1
    Join Date
    Jul 2012
    Posts
    4
    Post Likes

    Checking blower motor

    I'm new to this forum, and relatively new to hvac within the last 4 months or so. I've taken a fundamentals hvac class to get my EPA and learned the basics in residential HVAC systems and operations.

    I'm trying to learn as much as I can to become a service technician for my company. I currently work with others but would like to impress my boss and learn as much as I can to be able to go out on my own as my experience grows.

    I was wondering if you guys could tell me the sequence on checking whether or not a blower motor is bad or if its just a capacitor problem. This maybe an easy question but I'd like to know for sure so some day I can diagnose quickly whether its a capacitor problem, a motor problem or a board problem, ect.

    Share your wisdom please!

  2. #2
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    A quick way to check is manually start the blower wheel then apply power. You may need to jumper R to G then plug the unit it while the blower is still spinning from your manual start. If the motor runs you have a bad cap. Be VERY careful using this method, done wrong it can take fingers off !!!

  3. #3
    Join Date
    Jul 2012
    Location
    South Carolina
    Posts
    7
    Post Likes
    If the motor should be running and its not, use a multi meter to see if you have 24V between G & C. If you have 24V make sure you are getting the proper voltage to the motor (120V, 240V depending on what your working on) To do this check between the fan speed wire and the common wire that go to the motor. If you have the proper voltage. Turn off power to the unit and check the capacitor. If the capacitor is good then the motor is bad. (this is a very basic discription) I would recommend to someone new to get comfortable using your meter. It will be your best friend. Hope this helps.

  4. #4
    Join Date
    Jan 2012
    Location
    WEST COLUMBIA S.C.
    Posts
    293
    Post Likes
    Check microfarads of capacitor. Also u can check all windings using a ohmmeter

  5. #5
    Join Date
    Jul 2012
    Posts
    4
    Post Likes
    Thread Starter
    Thanks guys, I appreciate it!

  6. #6
    Join Date
    Jul 2012
    Location
    Stratford
    Posts
    27
    Post Likes
    Just ran into this today. Unit Was buzzing When i got there. Compressor or motor? Fan spun easily. I threw a hard start on to see if I could get the motor to start. Wouldn't go but pulled the compressor in. Got the capacitor tester and of course the capacitor was no good. Those testers help if your not sure. Very simple test.

  7. #7
    Join Date
    Jul 2012
    Location
    Phoenix, AZ
    Posts
    40
    Post Likes
    Yeah I would 24v first and then check your main voltge at the contactor. If everything reads out fine then check your cap. These are a few steps that I use.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •