    Have any of you used this "Cliplight" sealant on heat pumps? I'm considering putting it in a unit that I have been unable to locate the leak. I have some serious reservations about using this stuff but I've tried fluorescent dye and pressure testing with nitrogen on this particular system without any success.

    [Edited by nratom45-70 on 08-19-2006 at 09:36 PM]

  2. #2
    Join Date
    Jan 2001
    Posts
    7,487
    If you cant find the leak then it must be very very very very small.....I wouldnt put anything in that system thats designed to clog up an orifice....

    How much does it leak.... Have you tried isolating parts of the system and checking.... remove the evap coil and hose it down real good with soap... Ive pulled condenser coils before and evapoators and put them in a bathtub full of water before to find leaks.... seal off both ends of the tubing and check the line set at increased pressure...

    A good leak detector should find it....

    I wouldnt use dye either...but thats just me.

  3. #3
    Join Date
    Jul 2005
    Location
    USA
    Posts
    780
    Thanks for the ideas. I did a search on this site and found some negative comments about sealers, so I am NOT going to put that stuff in there. My main problem is that I'm the only service tech for our company which does over a million dollars a year in business, I average 7-8 calls a day and am not able to spend a lot of time on one call ( I know, my employer needs to hire more help......he has and they either don't know anything or they don't want to work overtime/nights/ weekends. Everytime we hire one, they last from 6 weeks to 9 months on average).

  4. #4
    Join Date
    Nov 2005
    Location
    Kansas
    Posts
    4,411
    I used the sealant in two old systems with success this summer. I will use it again in old systems to get some more life out of it.

  5. #5
    Join Date
    Nov 2005
    Location
    Kansas
    Posts
    4,411
    Originally posted by corny
    I wouldnt put anything in that system thats designed to clog up an orifice....
    Could you elaborate a bit more about that...it's news to me, I thought it would need some air to react and I don't know how it would have anything to do with the orifice.

  6. #6
    Join Date
    Aug 2006
    Location
    grand rapids,michigan
    Posts
    14

    Wink

    great stuff. used it for a couple of years no problems,however some of the problems stated more than likley occured w/improper install of sealent you must pay close attention to the directions. install differs from r-22vs410-a.amazing had a leak on 90 fitt at line termination in wall(could see refer bubbling out) options were leakseal or cut out wall to repair leak(inside finished).installed leakseal.returned year later for tune up leak sealed refrigerant charge fine.
    THE DAY YA THINK YA KNOW IT ALL IS THE DAY YA STOP LEARNING

  7. #7
    Join Date
    Sep 2005
    Location
    Massachusetts
    Posts
    25
    Has anyone used the product Big Blu?

    http://www.refrigtech.com/bigblumanual1.html


  8. #8
    Join Date
    Nov 2005
    Location
    Kansas
    Posts
    4,411
    yes, I wish the bubbles would be that big.

  9. #9
    Join Date
    Jul 2005
    Location
    USA
    Posts
    780
    Yes, Big Blue works pretty well.

  10. #10
    Join Date
    Feb 2002
    Posts
    516
    I have a customer who has an early '99 vintage 2 Ton geo HP that started having to be recharged every 6 mos starting Jan 05. Another service person recharged it on 8/14. They added a can of "Leak Stop" (Cliplight Super Seal) with the recharge. During the night of 8/17 the system quit cooling. The service person returned on the 18th to check the no cooling. They said that the compressor would have to be replaced. I was called for a second opinion. The compressor was locked, just draw locked rotor. The system is out of the 5 year warranty, so now what does the customer do? Replace the evaporator coil (which is probably where the leak is) and the compressor? What about the Super Seal that's still in the HX and other piping? What affect will it have on the TXV and reversing valve? What kind of warranty can I provide on the replacement of the parts? Or does the customer buy a new HP? Also, the compressor had a SPP-6 soft hard start kit on it--previous problems with the compressor not wanting to start correctly? It's a Tech AW5519EXN with OEM piping.

  11. #11
    Join Date
    Jan 2005
    Location
    Perth - Western Australia
    Posts
    775
    I have an idea. i have never believed in these type of fixes or used them, but maybee they have a place. we all go to the decrepit systems with condenrer on last leg & evap leaking & the cheap ass h.o. wanting us to juice it up a few times cause they refuse to replace the system.
    well why not put this crap in casue when it causes the compresser to **** the bed, they no longer can call you & try to get you to gas there piece of crap up, we will only gas & go once for a customer at there request. this could possibly end those fools calling to have refrigerant put in there piece of crap. lol
    The Captain.

  12. #12
    Join Date
    Jul 2005
    Location
    USA
    Posts
    780
    That's an idea!!!!!!!!!!!!!!

  13. #13
    Join Date
    Nov 2000
    Location
    Upstate, SC
    Posts
    2,919
    Maybe. We've used the sealant in 6 systems since we have known about it. One was a leak in a lineset on a new system that we could not get back to because of the expense of tearing out the wall. I discussed the stuff with the customer and they okayed it. That was two years ago and it has ran fine since. Another was a leak in a almost new 50 ton coil. The customer was willing to try it rather than go to the trouble and expense of changing the coil again and it has ran all summer without a problem. The other four systems we put the stuff in were systems that were worn out and ready to be changed, but they were running except for the leak. All four of those have since died and been changed out, but I can't say if the sealant did them in, or just old age. All those times being low on freon didn't do them any good either. Just hard to say...

    Bobby