Thread: High suction, low discharge

  1. #1
    Join Date
    Mar 2003
    Location
    austin
    Posts
    451
    Post Likes

    High suction, low discharge

    So I just installed a complete Rheem 5 ton, 14ajm series system ast november. HO tells me its not cooling as good. I arrive to find a loud compressor, 200 psi suction and 275 head. First thing that comes to mind is bad valves. A few minutes later the compressor cuts off on internal overload. I take a hose and cool it off. 10 min later, compressor kicks back on and pressures now seem normal (130/325) 13 subcool , 19 delta t. So I let it run for 20 minutes and take off. An hour later , HO called back and outdoor unit has stoppes running again. Bad txv?
    when life throws me a banjo, i play it

  2. #2
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,312
    Post Likes
    Why would you leave with a compressor running 225/200 without resolving the issue ?

    Of course its going to trip again.

  3. #3
    Join Date
    Jan 2007
    Location
    in my lumpy chair
    Posts
    1,975
    Post Likes
    Overfeed. possible loose bulb or poorly insulated, over sized.
    Suction pressure high, head pressure low, superheat low, subcooling low, amp low.
    I don't see any superheat or subcooling
    I dont warranty Tinkeritus

  4. #4
    Join Date
    Mar 2003
    Location
    austin
    Posts
    451
    Post Likes
    Thread Starter
    Quote Originally Posted by Six View Post
    Why would you leave with a compressor running 225/200 without resolving the issue ?

    Of course its going to trip again.
    I was planning on going back to replace the txv. Just wanted some feedback
    when life throws me a banjo, i play it

  5. #5
    Join Date
    Oct 2010
    Location
    Texas
    Posts
    43
    Post Likes
    Is the suction line very cold? If not I would suspect the internal releif valve in the compressor.

  6. #6
    Join Date
    Oct 2010
    Location
    Texas
    Posts
    43
    Post Likes
    My above question applies when the unit is malfunctioning. I'm assuming the condenser fan was running? Condenser fan shutting off, when your not there? Check fan amps and the cap.

  7. #7
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,312
    Post Likes
    Quote Originally Posted by michigan1 View Post
    I was planning on going back to replace the txv. Just wanted some feedback
    Ah...ok.

    Well someone mentioned a week internal relief that sounds reasonable.

    Even if your txv was wide open you wouldnt be equalizing like that.

    It almost sounds like its a scroll running backwards.

  8. #8
    Join Date
    May 2008
    Location
    Myrtle Creek. Oregon
    Posts
    182
    Post Likes
    bad valves or internal releaf open
    a stupid question is a question you wont to ask, but don't

  9. #9
    Join Date
    Oct 2010
    Location
    Texas
    Posts
    43
    Post Likes
    If bad valves, it wouldn't have returned to normal pressures.

  10. #10
    Join Date
    Mar 2003
    Location
    austin
    Posts
    451
    Post Likes
    Thread Starter

    Confused

    Quote Originally Posted by tharding54 View Post
    If bad valves, it wouldn't have returned to normal pressures.
    Exactly
    when life throws me a banjo, i play it

  11. #11
    Join Date
    Mar 2003
    Location
    austin
    Posts
    451
    Post Likes
    Thread Starter
    Quote Originally Posted by tharding54 View Post
    Is the suction line very cold? If not I would suspect the internal releif valve in the compressor.
    Ok this makes sense. IRV pops, compressor gets hot, then goes off on internal overload? Ive never had one do that but logical...
    when life throws me a banjo, i play it

  12. #12
    Join Date
    Dec 2010
    Location
    Palm Beach,Fl.
    Posts
    1,091
    Post Likes
    Sounds like a scroll running backwards to me as well. I was working on unit the other day and we had a little power brown out and the neighbors rheem unit started running backwards. I reset the breaker and it started up fine. Maybe they have a bad connection or floatswitch that is causing the unit to short cycle. Install a time delay and check your wiring inside and and out.
    Quote Originally Posted by k-fridge View Post
    The laws of physics know no brand names.

  13. #13
    Join Date
    Mar 2003
    Location
    austin
    Posts
    451
    Post Likes
    Thread Starter
    Quote Originally Posted by SoFlaDave View Post
    Sounds like a scroll running backwards to me as well. I was working on unit the other day and we had a little power brown out and the neighbors rheem unit started running backwards. I reset the breaker and it started up fine. Maybe they have a bad connection or floatswitch that is causing the unit to short cycle. Install a time delay and check your wiring inside and and out.
    Its single phase. You mean its running backwards on overload?
    when life throws me a banjo, i play it

  14. #14
    Join Date
    Dec 2010
    Location
    Palm Beach,Fl.
    Posts
    1,091
    Post Likes
    During a very brief power interruption (brown out) the expansion of gas in the compressor can start moving the rotor in reverse. If power is applied during that rotation it is possible for the motor to start running backwards until it overheats and it can do damage to the scroll. It can't pump so the motor isn't cooled by the suction vapor anymore. I had heard that Copeland fixed this issue at some point, but I still see it on equipement built in the last 5 years. For the record, I have only seen this happen to Copeland scrolls.
    Quote Originally Posted by k-fridge View Post
    The laws of physics know no brand names.

  15. #15
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by SoFlaDave View Post
    During a very brief power interruption (brown out) the expansion of gas in the compressor can start moving the rotor in reverse. If power is applied during that rotation it is possible for the motor to start running backwards until it overheats and it can do damage to the scroll. It can't pump so the motor isn't cooled by the suction vapor anymore. I had heard that Copeland fixed this issue at some point, but I still see it on equipement built in the last 5 years. For the record, I have only seen this happen to Copeland scrolls.
    I'm with Dave.

    I'd take the proactive step of installing a time delay.

    For me, the "loud compressor" you mentioned right out of the box, along with the pressures, suggests to me it is getting started in the wrong direction. A time delay will help inhibit that effect.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  16. #16
    Join Date
    Mar 2003
    Location
    austin
    Posts
    451
    Post Likes
    Thread Starter
    Quote Originally Posted by timebuilder View Post
    I'm with Dave.

    I'd take the proactive step of installing a time delay.

    For me, the "loud compressor" you mentioned right out of the box, along with the pressures, suggests to me it is getting started in the wrong direction. A time delay will help inhibit that effect.
    Thougjt the visionpro stat had a time delay but it very well could be disabled. Thanks.
    when life throws me a banjo, i play it

  17. #17
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by michigan1 View Post
    Thougjt the visionpro stat had a time delay but it very well could be disabled. Thanks.
    It has it, and it is adjustable in installer setup.

    BUT, it works based on when it (the stat) turns the compressor off ITSELF, or when it "wakes up" from a full power down.

    If power is lost, the backup batteries don't let the stat know the compressor stopped, so it will come back on as soon as power is restored.

    I think the time delay is a better choice than taking out the batteries, as most HO's would not like to have to reprogram the stat for time whenever the power goes off.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  18. #18
    Join Date
    Jul 2012
    Location
    Baton Rouge Louisiana
    Posts
    179
    Post Likes
    I had one do that same exact thing tuesday. 11 year old Ruud 3 ton. Except it was running great, good pressures, subcool, superheat, delta T. It never shut off. Pressures went to about 200/275 compressor got REALLY hot. Was rated for 16.5 amps and was pulling 11.5 on one hot leg 3.5 on another. It had a leak in the evap coil and HO just wanted a whole new system

  19. #19
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,312
    Post Likes
    What about installing a 5-2-1 on the unit ? Wouldn't it increase starting torque ?

    Also a delay on make timer is cheap too if you want a no fail delay.

  20. #20
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,881
    Post Likes
    older scrolls had a habit of starting up and running backwards due to a momentary loss of power. newer ones are not supposed to do that but it sounds like yours might be.
    i would try putting a delay on break timer right before the contactor, only needs to be set for 15 seconds or so to prevent reverse running from happening.

    something to try and much easier than a txv.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •