High suction, low discharge
So I just installed a complete Rheem 5 ton, 14ajm series system ast november. HO tells me its not cooling as good. I arrive to find a loud compressor, 200 psi suction and 275 head. First thing that comes to mind is bad valves. A few minutes later the compressor cuts off on internal overload. I take a hose and cool it off. 10 min later, compressor kicks back on and pressures now seem normal (130/325) 13 subcool , 19 delta t. So I let it run for 20 minutes and take off. An hour later , HO called back and outdoor unit has stoppes running again. Bad txv?
when life throws me a banjo, i play it
-
08-03-2012, 10:30 AM #2
Why would you leave with a compressor running 225/200 without resolving the issue ?
Of course its going to trip again.
-
08-03-2012, 10:34 AM #3
Overfeed. possible loose bulb or poorly insulated, over sized.
Suction pressure high, head pressure low, superheat low, subcooling low, amp low.
I don't see any superheat or subcoolingI dont warranty Tinkeritus
-
08-03-2012, 10:35 AM #4
Professional Member
- Join Date
- Mar 2003
- Location
- austin
- Posts
- 232
-
08-03-2012, 10:48 AM #5
Professional Member
- Join Date
- Oct 2010
- Location
- Texas
- Posts
- 37
Is the suction line very cold? If not I would suspect the internal releif valve in the compressor.
-
08-03-2012, 11:01 AM #6
Professional Member
- Join Date
- Oct 2010
- Location
- Texas
- Posts
- 37
My above question applies when the unit is malfunctioning. I'm assuming the condenser fan was running? Condenser fan shutting off, when your not there? Check fan amps and the cap.
-
08-03-2012, 12:33 PM #7
-
08-03-2012, 12:50 PM #8
Professional Member*
- Join Date
- May 2008
- Location
- Myrtle Creek. Oregon
- Posts
- 182
bad valves or internal releaf open
a stupid question is a question you wont to ask, but don't
-
08-03-2012, 12:52 PM #9
Professional Member
- Join Date
- Oct 2010
- Location
- Texas
- Posts
- 37
If bad valves, it wouldn't have returned to normal pressures.
-
08-03-2012, 01:35 PM #10
Professional Member
- Join Date
- Mar 2003
- Location
- austin
- Posts
- 232
-
08-03-2012, 01:39 PM #11
Professional Member
- Join Date
- Mar 2003
- Location
- austin
- Posts
- 232
-
08-03-2012, 01:43 PM #12
Professional Member*
- Join Date
- Dec 2010
- Location
- Palm Beach,Fl.
- Posts
- 870
Sounds like a scroll running backwards to me as well. I was working on unit the other day and we had a little power brown out and the neighbors rheem unit started running backwards. I reset the breaker and it started up fine. Maybe they have a bad connection or floatswitch that is causing the unit to short cycle. Install a time delay and check your wiring inside and and out.
-