    Got called out to look at a walk in at a gas station and found this gem. We got outbid on the condenser install and this is what they got. See anything missing?

    Evap coil was not changed, and old unit had burnt up compressor.

  2. #2
    Join Date
    Jan 2013
    Location
    New Jersey
    Posts
    33
    Liquid and suction drier?

  3. #3
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    2,030
    Im guessing a disconnect?

  4. #4
    Join Date
    Oct 2012
    Location
    Smallville
    Posts
    120
    Yup, filter driers. They installed the new condenser and put no filters on at all.

  5. #5
    Join Date
    Aug 2012
    Posts
    2,643
    Filter could be out of sight. defiantly should have a suction line FD. Disconnect could be within eyeshot.
    My name is TooCoolforschool and I am a chronic over charger.

  6. #6
    Join Date
    Jan 2013
    Location
    New Jersey
    Posts
    33
    Well they'll be replacing it soon again anyway. Maybe you get the bid next time. Or with any luck a compressor change.

  7. #7
    Join Date
    Jan 2004
    Location
    Here and there
    Posts
    4,804
    I always like the liquid drier inside by the evap.
    i belong to peta ... people eating tasty animals. all my opinions are just mine.

  8. #8
    Join Date
    Oct 2012
    Location
    Smallville
    Posts
    120
    Checked inside at the Evap. Wasn't touched. They left the old lines to the inside and just brazed new ends at the compressor

  9. #9
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,325
    If that's for a walk-in box, there's a lot more missing than just a filter-drier.

  10. #10
    Join Date
    Oct 2012
    Location
    Smallville
    Posts
    120
    No that's ac for the store. We were just there to look at the walk in. I worded that wrong.

    Probably should have had a cycle switch or some type of pressure control since it was 40 degrees today and running I would guess though.

  11. #11
    Join Date
    Oct 2012
    Location
    Smallville
    Posts
    120
    And yea it had a disconnect.

  12. #12
    Join Date
    Apr 2013
    Location
    Knoxville TN
    Posts
    53
    Some of those condenser have FD inside the cond.

  13. #13
    Join Date
    Sep 2005
    Location
    Atlanta GA area
    Posts
    21,057
    I do not see any low voltage wiring... Is it inside the conduit with the high voltage wiring (not legal in my state unless the wire is insulated for high voltage).
    GA-HVAC-Tech

    Quality work at a fair price with excellent customer service!

    Romans Ch's 5-6-7-8

    2 Chronicles 7:14

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event