    Distech UV-L Help.

    Its been a while since I've dealt with a configurable Distech and I'm having trouble trying to expose a point to command an output via Tridium AX.

    I see an "nviExtCmdOutput" but when I write to it, it takes the value, then reverts back to whatever value it was before.

    There are also state/value points called "OvrOutput" which will update the "Permit Override" tick and sets the value in the Wizard, but nothing happens.


    All I want to do is expose a method for the customer to override the output from a graphic in Tridium.

    Any help would be appreciated!

  2. #2
    Join Date
    Jul 2009
    Location
    Charlotte, NC
    Posts
    423
    I was able to figure this out.

    FYI.....nviRequest is the point used to put the controller in override mode.

  3. #3
    Join Date
    Jun 2012
    Location
    USA
    Posts
    52
    Thank you! That is the same reason that I am here today. Do I set the nviRequest to Manual? It is defaulted to Automatic. Thank you.