Trane Intellipak
Does anyone know if a bacnet card is available for an older (2001) Trane intellipak and can it be purchased by a non-trane company? I know the Comm5 Lontalk is available. Please help......
-
04-12-2011, 07:04 PM #2
Professional Member
- Join Date
- Nov 2007
- Posts
- 50
I believe the only way to get BacNet from that older I-Pak is through a BCU connected to it and the points converted from comm4 to BacNet. No comm card option.
-
04-13-2011, 10:00 PM #3
Professional Member
- Join Date
- Nov 2007
- Location
- Clayton, NC
- Posts
- 26
Older Intellipak
You can use the new Trane Bacnet module on older Intellipaks. I just added them to 5 1998 Intellipaks. There is a kit with additional parts needed. In addition to the bacnet module,the HI kepad has to be replaced as well as the main control board in the Intellipak. Its not a cheap conversion, but it can be done, and the BCU is not needed.
-
04-13-2011, 10:25 PM #4
-
04-14-2011, 02:20 PM #5
Professional Member
- Join Date
- Oct 2007
- Location
- Arizona DUH
- Posts
- 164
We are bidding a controls upgrade against Trane, I don't even think the bacnet will work. it appears the specification was written around the comm4 so they can see refrigerant temps and other points that I know Comm5 and Bacnet wont show. Unless I do go thru the BCU option, then I am so far out of wack on price I wouldn't have a shot anyway.....Thanks for the info....
-
04-14-2011, 03:35 PM #6
Professional Member
- Join Date
- Jun 2005
- Posts
- 285
Try a Jace with comm4 driver or lontalk driver.
-
07-20-2012, 12:21 AM #7
Regular Guest
- Join Date
- May 2006
- Location
- Seattle
- Posts
- 3
I am curious about how adding the BACnet (BCI-I) cards to the older Intellipaks went for you.
Are you able to see everything you can on the local human interface screen?
I am wondering if it is a valid option to adding our own sensors and utilizing the existing GBAS module which doesn't allow for much control or give back much information.
Thanks.
-
07-20-2012, 10:10 AM #8
Professional Member
- Join Date
- Nov 2007
- Location
- Clayton, NC
- Posts
- 26
Intellipak BCI-I
I see that evaporator and saturated refrigerant temps are listed as read points in the BCI-I literature. I these are the ones in your spec, then bacnet integration should work.