    Quote Originally Posted by LKJoel View Post
    Why the 45 degree angle?
    I had seen it done by manufacturers. I believe it's to ensure that liquid refrigerant is entering the capillary tube. I started to copy the idea.

  2. #15
    Join Date
    Aug 2012
    Location
    willowick ,oh
    Posts
    261
    Post Likes
    If you see there was work done on the refrig. side. i Would find the factory specs for the cap and the drier and replace both. Also i never re-use refrig. hopefully you put it back in the system through a drier.Check to see if it is a low temp comp if it is not the original.Good luck

  3. #16
    Join Date
    Jun 2003
    Location
    Tampa Bay, FL.
    Posts
    140
    Post Likes
    The two critical points to check for suction line kinks on these slide out skids are the last bend before it enters the compressor and right where it enters the refrigeration cabinet. Old copper becomes brittle with age and will kink easily in those spots. Also, if your cap tube is soldered to the suction line, it will throw off your superheat temp.

  4. #17
    Join Date
    Apr 2011
    Location
    michigan
    Posts
    175
    Post Likes
    Thread Starter
    No kinks in the suction line, the cap tube is not soldered to the suction line but wrapped around it and both are insulated. I didn't check the compressor to see if it was original or a low temp compressor, but the unit has been running fine now for a month, no complaints from the customer. Still havent been back to clean the ice machine they want to do it themselves, I just hope they do clean it I cant stand seeing crusty ice machines!

  5. #18
    Join Date
    Jun 2003
    Location
    Tampa Bay, FL.
    Posts
    140
    Post Likes
    Those fractional hermetics are real workhorses. I'm amazed at the abuse and neglect they suffer yet still keep pumping!Name:  ImageUploadedByTapatalk1344692434.469170.jpg
Views: 108
Size:  77.0 KBthis is just one example I run into!