Page 4 of 5 FirstFirst 12345 LastLast
Results 40 to 52 of 53
  1. #40
    Join Date
    Nov 2011
    Location
    East Side
    Posts
    3,946
    Post Likes
    Quote Originally Posted by cavalieri85 View Post
    so it doesnt rust out and leak!!!! and the closer to the txv the better any crud that could be in the lines from assembly will go into the drier not the txv
    not only that, but alot of times it's easier to get to inside if you have to change it in the future. and driers are supposed to be installed vertically, so they don't trap oil in the canister.....makes that easier too.

    nice install!

  2. #41
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,418
    Post Likes
    dries do not have to be installed vertically..... where is this info from...... and yes great work well done...
    it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair

  3. #42
    Join Date
    Nov 2011
    Location
    East Side
    Posts
    3,946
    Post Likes
    I didn't say they "had" to be......they are supposed to be.

  4. #43
    Join Date
    Aug 2008
    Location
    San Clemente, CA
    Posts
    1,421
    Post Likes
    They actually (manufactures) prefer them to be horizontally installed.

  5. #44
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,418
    Post Likes
    oh man...here we go...... does it really matter...i do not think so....
    it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair

  6. #45
    Join Date
    Aug 2008
    Location
    San Clemente, CA
    Posts
    1,421
    Post Likes
    Sportland Heat Pump filter drier:
    The drier may be installed in any position – vertical or horizontal
    – and with feed in either direction. Where possible, the horizontal
    position is preferred.


    Catch-All Filter-Driers are most effective in the liquid line. Place the
    filter-drier immediately ahead of other liquid line controls, such as the
    thermostatic expansion valve, solenoid valve, and See•All Moisture &
    Liquid Indicator. When applied in this way, the Catch-All provides
    maximum protection for the expansion valve and solenoid valve from
    dirt that may be in the system. If the system contains appreciable
    moisture, then this location gives the best results in protecting the
    expansion valve from freeze-up. If possible, place the filter-drier in a
    cold location. The acid removal ability of the Catch-All Filter-Drier is
    the same whether it is installed in the liquid line or suction line. End:

    Note they say to place the drier in a cold location, do you know why? This is a better environment for the drier to retain the moisture it has collected. By heating up the drier it can cause it to release the moisture it has collected. Having the drier outside in the sun is not a good location.

    Best practice:
    Place Heat Pump filter driers horizontal.
    Place all liquid line filter driers indoors just before the TXV in a cool indoor environment. "If possible, place the filter-drier in a
    cold location."
    Attached Images Attached Images

  7. #46
    Join Date
    Oct 2012
    Location
    staten island ny
    Posts
    2
    Post Likes

    Lightbulb

    nice install. real neat..I like it..

  8. #47
    Join Date
    Oct 2012
    Location
    staten island ny
    Posts
    2
    Post Likes
    Real neat.. I have always put the drier near the evap as well.. nice job!

  9. #48
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,418
    Post Likes
    Quote Originally Posted by JKopp View Post
    Sportland Heat Pump filter drier:
    The drier may be installed in any position – vertical or horizontal
    – and with feed in either direction. Where possible, the horizontal
    position is preferred.


    Catch-All Filter-Driers are most effective in the liquid line. Place the
    filter-drier immediately ahead of other liquid line controls, such as the
    thermostatic expansion valve, solenoid valve, and See•All Moisture &
    Liquid Indicator. When applied in this way, the Catch-All provides
    maximum protection for the expansion valve and solenoid valve from
    dirt that may be in the system. If the system contains appreciable
    moisture, then this location gives the best results in protecting the
    expansion valve from freeze-up. If possible, place the filter-drier in a
    cold location. The acid removal ability of the Catch-All Filter-Drier is
    the same whether it is installed in the liquid line or suction line. End:

    Note they say to place the drier in a cold location, do you know why? This is a better environment for the drier to retain the moisture it has collected. By heating up the drier it can cause it to release the moisture it has collected. Having the drier outside in the sun is not a good location.

    Best practice:
    Place Heat Pump filter driers horizontal.
    Place all liquid line filter driers indoors just before the TXV in a cool indoor environment. "If possible, place the filter-drier in a
    cold location."
    my 30 years in the trade says I do not agree.... i have never had a problem..... and I actually installed a drier inside the other day just to say I had done it .... guess what ...it worked like the thousands of other installs I have done...
    it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair

  10. #49
    Join Date
    Jan 2011
    Posts
    1,080
    Post Likes
    Thread Starter
    30 years and you haven't had a drier rust out and leak? I had several of them this summer.

  11. #50
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,418
    Post Likes
    never had one rust out..... have had a couple of expansion valves rust out .... no salt in the air here it freezes....lol
    it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair

  12. #51
    Join Date
    Aug 2008
    Location
    San Clemente, CA
    Posts
    1,421
    Post Likes
    If you pull good vacs and practice good workmanship it may not mater where the drier goes. I have been doing HVAC 35 years and I am still learning and doing what I learn. I have also had many outdoor filter driers rust out including suction accumulators.

  13. #52
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,418
    Post Likes
    no salt in Canada ....driers never rust out.....
    it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair

Page 4 of 5 FirstFirst 12345 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.