New header sweated in. Piece of cake. Light heat with 15%.
Pic of the old part (chopped up) and new header.
Vacuuuum....I leaked check with 150 psi nitro and snoop. Also replaced the drier....of course. The drier was NOT plugged.
Weigh in charge. Precious R22. 7.6 lbs according to Unit nameplate.
Running like a champ. 250/76...pressures before repair....270/40 and icing.
Last pic is from a Trane RTAA110. Chiller is located right off the bay. Was called out about a month ago on circuit A locking out on low suction super heat. Replaced sensors and STILL low suction super heat. These things only run 4 degrees SSH.
Condemened the EEV which means condemning BOTH EEVs AND MODULE after going through the EXV check spelled out in my Trane trouble shooting addendum.
Now each circuit has TWO sight glasses in series. Oh well at least there is a visual representation of the EEV working now.
Chiller runs fine now but it's incessant whining upsets the apartment block next door to the 6 story building it and it's two brothers are mounted on.