Results 14 to 22 of 22
    Sep 2011
    How does a colder coil slow the cooling process?
    Madison, WI/Cape Coral, FL
    Quote Originally Posted by wdshea View Post
    Colder coils reduce the btus per of cooling. Compressors pump less refrigerant at lower suction pressures.
    Regards TB
    Jul 2012
    Southwest
    I have witnessed humidity problems on fitness centers, lacking fresh air. You may be able to run one compressor fine without oil return problems.
    Contact the manufacturer to verify. Also, have the manufacturer engineer a way to downsize the tonnage..
    I would be concerned long term for that unit if it is that oversized.
    Quote Originally Posted by B1978 View Post
    There are many days where there is low/no cooling loads yet the outdoor dew points are above the acceptable indoor dew points. Plus the moistue the occupants add to the total moisture that must be removed. Over-cooling lowers the indoor temp which in turn increases the amount of moisture that must be removed to maintain low %RH. Supplemental dehumidification by high efficiency dehumidifier like the Ultra-Aire/Santa Fe/Hi-E Dry/Quest are a long term solution to provide ideal temp/%RH.
    Regards TB
    Jul 2012
    Southwest
    Could he add a ton of outside air to increase his load? Guess it depends on his region, whether he's in a humid area or not.
    NC
    If this is a new jail, are you at capacity yet? I would assume the engineers sized the unit based on maximum occupant capacity.
    Jul 2012
    The space needs to have positive pressure, but not too much. Make sure you have some make up air (approx 10%).
    You need to run on 1 stage, cycling 2nd stage as needed. If you can control 2 stages of blower speed to go with your 2 stages of compressors, that would be ideal.
    Mount Airy, MD
    Quote Originally Posted by Blows_Sucks_Heats_Cools View Post
    Codes for Jails/Prisons are not going to allow you to cut back on outside air, they want 100% ODA and the air changes to boot.
    Hekp us understand how we are going to control %RH during 60-70^F dew point outside air during low/no cooling condition? Like we need latent cooling with much sensible cooling.
    Regards TB