Results 1 to 12 of 12
    Dec 2011
    TN
    Confused Oversized/humidity problems
    Hello everyone. I have a 15 ton J15PC heatpump in an Commerical building. This was a designed and engineered building. I believe the unit is oversized but getting someone to admit that is not going to happen. Only runs for a couple of min and is satisfied. Humidity is verrrry high. Do yall have an suggestion on how to control the humidity without over cooling. I am up for any thing we are talking about dumping a lot of air in the ceiling to put a load on the system...
    Madison, WI/Cape Coral, FL
    What is the temp/%RH? Coil temp during cooling?
    regards TB
    Virginia
    Is building occupied or vacant
    Dec 2011
    TN
    Yes it is vacant it is jail pod 72 temp with about 64% humidy and higher
    Dec 2010
    Palm Beach,Fl.
    If its vacant than that's part of the issue. If you try to remedy the issue while it's vacant you'll be scrambling to reverse it when it's occupied. Might be able to adjust the pulleys for lower air flow.
    Quote Originally Posted by k-fridge View Post
    The laws of physics know no brand names.
    Dec 2011
    TN
    I am sorry it occupied I don't know why I said it was vacant
    Jan 2011
    Central PA
    i am assuming the unit is staged. what is the tonnage of each stage?
    Saint Joseph, MI
    Quote Originally Posted by jabeu View Post
    That was my thought. A unit that size should have 2 compressors with 2 refrigerant circuits.
    The only other thought is doing something unusual like install a smaller unit, maybe 5 tons in parallel with backflow dampers of course as a first stage.
    TACKERDOWN
    Additional infractions may result in loss of posting privileges.
    Your post has been deleted.
    Jul 2012
    turn the thermostat
    This is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise, questions, or commentary in other peoples threads here. Please apply to the AOPC today, thank you.
    Apr 2012
    Paper Street Soap Company
    There are single stage 15 ton units.
    I cant imagine its good for that semi hermetic compressor either.
    You're going to have to provide some form of reheat with humidistats to control humidity.
    Quote Originally Posted by Six View Post
    Do your reheat with a couple of 200 lbs. per day dehumidifiers like the Ultra-Aire XL200 H. They remove 8 lbs. hour per unit and provide 12,000 btus per reheat per unit. With a good setup on the a/c, expect to to be able to remove upto 80lbs. of moisture per hour with dehus and a/c operating. The 24,000 btus of reheat uses 2 Kw of electricity.
    Regards TB