    Airflow and system capacity

    So if i have a 2 ton split system r410 with 700 cfm across the coil system charged correct with a 18 degree temp drop across the coil and i adjust airflow to 900 cfm adjust charge and have a 16 degree temp drop across the coil which is the better system as far as total capacity?

  2. #2
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    1,188
    At 18/700 cfm your getting 13,600, at 16/900cfm you get 15,500 ~ Sensible. This does not say anything about what is happening to your latient. YOu need to get a wet bulb measurement to get the total capacity.

    Formula'a are CFM x 1.08 x temp drop = sensible. CFM x 4.5 x enthalpy drop = total heat.

  3. #3
    Join Date
    Mar 2003
    Posts
    76
    To figure capacity the formula is - enthalpy difference x 4.5 x cfm

    to get the enthalpy difference you need the webulb readings then you can convert that to enthalpy using a calculator

    with air conditioners most people adjust airflow to 350-400 cfm and heat pumps around 400-450 cfm

    with the lower range of airflow you gain better humidity control

  4. #4
    Join Date
    Mar 2003
    Posts
    76
    Quote Originally Posted by kls-ccc View Post
    At 18/700 cfm your getting 13,600, at 16/900cfm you get 15,500 ~ Sensible. This does not say anything about what is happening to your latient. YOu need to get a wet bulb measurement to get the total capacity.

    Formula'a are CFM x 1.08 x temp drop = sensible. CFM x 4.5 x enthalpy drop = total heat.
    you beat me to the punch

  5. #5
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,294
    Delta T is not an indicator of a proper charge

  6. #6
    Join Date
    Apr 2012
    Location
    Millsboro, DE
    Posts
    86
    Designwise, 350 CFM/Ton is used in moist climates (less sensible, more latent), 450 is used in dry climates (more sensible, less latent). 450 provides higher total cooling.

  7. #7
    Join Date
    Aug 2003
    Posts
    418
    Thanks for all the good info,i am running into alot of systems that the airflow is either way to high or set on low speed and with days of 90 degrees an above a system not set up right on installation is having issues.i had one 2.5 ton system running at 800 cfm with a 18 degree temp drop that ran almost all day,i got the airflow right and the temp drop was 16 and it would cycle at 74 degrees on a 90 degree day and it never did that before.

  8. #8
    Join Date
    Jan 2009
    Location
    Keokuk, IA
    Posts
    5,328
    Ideally, you use dehumidification on demand and slow the blower when more latent capacity is needed. Otherwise you have to find a best compromise between sensible and latent capacity.

    On the systme above, the perfect point might be somewhere inbetween. Maybe 900-950CFM on a 2.5 ton system so it has enough sensible for desing conditions, but enough latent for cooler weather.

  9. #9
    Join Date
    Nov 2004
    Location
    NJ
    Posts
    1,165
    Total capacity will be higher with a higher sensible heat ratio. Higher air flow will give you a higher SHR, lower airflow produces a lower SHR. You should match the SHR of your equipment to the SHR of the space you are trying to condition.
    Ed J

  10. #10
    Join Date
    Jan 2012
    Location
    WEST COLUMBIA S.C.
    Posts
    205
    What method did you use to get your cfm

  11. #11
    Join Date
    Jan 2007
    Location
    Mn the state where absolutey nothing is allowed
    Posts
    1,124
    Quote Originally Posted by Ed Janowiak View Post
    Total capacity will be higher with a higher sensible heat ratio. Higher air flow will give you a higher SHR, lower airflow produces a lower SHR. You should match the SHR of your equipment to the SHR of the space you are trying to condition.

    Ed, what do you mean by" the SHR of the space" ??

    are you talking design conditions?

    ive been living and breathing capacity calculations this year to learn and the more i do the more i find myself not trusting rated airflow by dipswitchs or blower curves/TESP
    my boss thinks its possible to repeal the laws of physics

  12. #12
    Join Date
    Nov 2004
    Location
    NJ
    Posts
    1,165
    Your total gain is the sensible gain plus the latent gain. If you divide the total gain into the sensible gain it will give the SHR of the space (sensible to latent ratio).

    A "perfect" match is a system with the equpitments SHR matching the spaces SHR.
    Ed J

  13. #13
    Join Date
    Jan 2007
    Location
    Mn the state where absolutey nothing is allowed
    Posts
    1,124
    thx Ed, i was afraid your were going to say MAN J........
    my boss thinks its possible to repeal the laws of physics