Thread: Airflow and system capacity
-
07-17-2012, 08:25 AM #1
Professional Member
- Join Date
- Aug 2003
- Posts
- 418
Airflow and system capacity
So if i have a 2 ton split system r410 with 700 cfm across the coil system charged correct with a 18 degree temp drop across the coil and i adjust airflow to 900 cfm adjust charge and have a 16 degree temp drop across the coil which is the better system as far as total capacity?
-
07-17-2012, 08:40 AM #2
At 18/700 cfm your getting 13,600, at 16/900cfm you get 15,500 ~ Sensible. This does not say anything about what is happening to your latient. YOu need to get a wet bulb measurement to get the total capacity.
Formula'a are CFM x 1.08 x temp drop = sensible. CFM x 4.5 x enthalpy drop = total heat.
-
07-17-2012, 08:55 AM #3
To figure capacity the formula is - enthalpy difference x 4.5 x cfm
to get the enthalpy difference you need the webulb readings then you can convert that to enthalpy using a calculator
with air conditioners most people adjust airflow to 350-400 cfm and heat pumps around 400-450 cfm
with the lower range of airflow you gain better humidity control
-
07-17-2012, 08:56 AM #4
-
07-17-2012, 09:00 AM #5
Delta T is not an indicator of a proper charge
-
07-17-2012, 09:31 AM #6
Professional Member*
- Join Date
- Apr 2012
- Location
- Millsboro, DE
- Posts
- 86
Designwise, 350 CFM/Ton is used in moist climates (less sensible, more latent), 450 is used in dry climates (more sensible, less latent). 450 provides higher total cooling.
-
07-17-2012, 10:08 AM #7
Professional Member
- Join Date
- Aug 2003
- Posts
- 418
Thanks for all the good info,i am running into alot of systems that the airflow is either way to high or set on low speed and with days of 90 degrees an above a system not set up right on installation is having issues.i had one 2.5 ton system running at 800 cfm with a 18 degree temp drop that ran almost all day,i got the airflow right and the temp drop was 16 and it would cycle at 74 degrees on a 90 degree day and it never did that before.
-
07-17-2012, 10:19 AM #8
Ideally, you use dehumidification on demand and slow the blower when more latent capacity is needed. Otherwise you have to find a best compromise between sensible and latent capacity.
On the systme above, the perfect point might be somewhere inbetween. Maybe 900-950CFM on a 2.5 ton system so it has enough sensible for desing conditions, but enough latent for cooler weather.
-
07-18-2012, 04:18 PM #9
Total capacity will be higher with a higher sensible heat ratio. Higher air flow will give you a higher SHR, lower airflow produces a lower SHR. You should match the SHR of your equipment to the SHR of the space you are trying to condition.
Ed J
-
07-18-2012, 09:01 PM #10
Professional Member*
- Join Date
- Jan 2012
- Location
- WEST COLUMBIA S.C.
- Posts
- 205
What method did you use to get your cfm
-
07-18-2012, 09:07 PM #11
Professional Member
- Join Date
- Jan 2007
- Location
- Mn the state where absolutey nothing is allowed
- Posts
- 1,126
my boss thinks its possible to repeal the laws of physics
-
07-18-2012, 09:28 PM #12
Your total gain is the sensible gain plus the latent gain. If you divide the total gain into the sensible gain it will give the SHR of the space (sensible to latent ratio).
A "perfect" match is a system with the equpitments SHR matching the spaces SHR.Ed J
-
07-18-2012, 09:44 PM #13
Professional Member
- Join Date
- Jan 2007
- Location
- Mn the state where absolutey nothing is allowed
- Posts
- 1,126
thx Ed, i was afraid your were going to say MAN J........
my boss thinks its possible to repeal the laws of physics


Reply With Quote